how much load 15kva dg set can bear
Answers were Sorted based on User's Feedback
Answer / jax
Sorry in above answer I have written wrongly. It is 12 kW.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / vikas m sampath
convert the kva to kw first ie kva*pf=kw so here 15*.8,(say pf is .8)now the ans is 12kw so up to 24amps out of this generator company say u got to put in only 80percent load of 24amps so about 19amps u can load for economy
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / jax
Normally DG is rated for 0.8 pf. So DG can bear upto 15 kW.
For any doubt in electrical please contact
jaxp333@yahoo.co.in
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / tanvir
15 kva dg set can use for 25 amp 3 phase load with
calculation of power factor 0.8.
Is This Answer Correct ? | 9 Yes | 10 No |
Why power factor does not occur in DG set ?
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
What is Exact meaning for Full load Efficiency and Maximum Efficiency of Transformer? Is there any Difference between? If yes ,please provide with formulae?
What are the advantages and disadvantages of the dc motors?
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
what are transmission line parameters and transmission line constants?
what is the ambient temperature of transformer oil & winding?
why dc moter are not earthed ????
1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is the reason for low voltage in houses? 3.Wat is meant by current and voltage? wat is difference between the two?
what is the difference between earthing and unearth
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
For a certain load i need 100kw load ,In that case what rating mccb should i use?