Answer / naresh kumar
Reasons:
1)to reduce the conductor size of the feeder.... i.e, by
increasing the voltage levels the current level decreases to
maintain constant power.. the feeder design depends on the
current levels so lesser currents lesser will be the cross
section...
2)by increasing the voltage levels the current levels
decreases so the i^2 R losses decreases and the transmission
efficiency increases.
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / d
High Voltage transmission has high Efficiency as far as the
transmission loss is considered
| Is This Answer Correct ? | 4 Yes | 1 No |
What do you mean by an instrument transformer?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
Define damping ratio.
why the voltage transmission is always in a multiple of 11? e.g. 110 V, 220 V, 33 kVA, 11 kVA
what is the difference between synchronous motor and induction motor?
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
why only 26v dc is used in aircraft and 115v ac in aircraft.
Why does the DC voltage needed is less than AC needed to produce corona?
induction motor. we have a three phase supply from diffrent source like R= transformer. Y = DG sets. B = ups. if motor is runing.
Alternating voltage and current is which type of quantities?
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
what things to be considered when designing UPS
0 Answers Aplab, Veta Kipawa ICT Center,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)