Answer / srikanthgss
I think ... since its a 5 MVA transformer , you can have a
unity pf load of 5kw or 4.5mw at 0.9 pf lag or 4.0mw load at
0.8 pf lag .
{ P=VIcos@
Given VI= 5MVA
=> at 0.9pf = 5*0.9=4.5MW
at 0.8pf = 5*0.8=4.0MW
..... etc .
}
| Is This Answer Correct ? | 75 Yes | 7 No |
Transformer have an interesting characteristics ie
You can Load the transformer around 20 % of Full load to
around 120% of full load without any problems(At that time
efficiency lie between 75 to 95 %).But maximum
efficiency will give when copper loss equal to core loss that
is around 80 to 85 % of full load.just see load vs efficiency
curve, then u ll b more clear.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / dharmendra
(
Load calculation for 3 phase ac motor
A = 1000 × P(kW) / (√3 × PF × VL-L(V)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.sri405
MVA is the apparent power means combination of active and
reactive power. Load means active power so 5 MVA capacity
means we can load this transformer below 5 mw.if there is a
completely resistive load than it may be loaded upto 5 mw
but practically it is not possible.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ramesh
KW = KVA x pf
1mva=1000kva
kva*0.8= kw
5*0.8=4kw
1kw= 1000W
4=1000*4=4000kw
5mva= 4mw or4000w
--RAMESH
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / addicted to know electrical
Load means current,not Mw(power).So,by looking at
P=VI*p.f....
Since i is load which is always variable....the power drawn
from the transformer will always vary......and hence it is
not inour hand how much load shall be given to the
transformer but the efficiency will be max. when load is
equal to iron loss divided by square of secondary
resistance.
| Is This Answer Correct ? | 2 Yes | 23 No |
Does the isolator has a making capacity????????
EXPLAIN METOD OF IMAGE OF TRANSMISSION LINE/ WHAT ARE ITS PRACTICAL APPLICATION?
what are the protection for DG set and why?
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
How to reduce power factor correction capacitors failure in an industrial environment with vsd and computers usage in the system
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
3 Answers Infotech, Vijai Electricals,
IS THERE ANY ELECTRONIC CIRCUIT TO REDUCE THE NEUTRAL TO EARTH VOLTAGE BELOW 3V ?
Neutral to earth and phase to earth voltage how much.
wat is the difference between rotor 1st stage fault and 2nd stage fault?
expansion of rccb
In which working principal temperature transmitter work.explain in detailed.
How to get a multiplier in 11kv energy meter?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)