what is the maximum load on for 10 kva & 25 kva transformer
Answers were Sorted based on User's Feedback
Answer / sandep
load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw
| Is This Answer Correct ? | 49 Yes | 10 No |
Answer / aruloli
Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.
If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .
primary load current is calculated as
P=VI
10*1000(VA)=230*I
I=43.47 A
Secondary current is ,
90.90 A
Considering Transformer as 3 phase, then
P=1.732*v*I
Primary load current is
10000=1.732*230*I
I=25.10 A
Secondary is,
52.48 A
| Is This Answer Correct ? | 35 Yes | 15 No |
Answer / k.sri405
10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kaleem
aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / dkverma67
For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / pillay
the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.
| Is This Answer Correct ? | 5 Yes | 6 No |
How to test lightning Arrester?
The cable area of cross section is 185 sq mm. How to convert this to the diameter.
How to measure current and voltage in an ELV circuit
which types of tests are required after commissioning of 6.6 kva tranformer?
when will be the iocl interview results ifaced the interview on september 8 th
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV
Why can't we take NO LOAD TRIAL of motors having V1 mounting??
3.7 kw motor ,how much sq mm cabel want to bare this motor load
what is the voltage regulation constant of ACSR Raccoon conductor
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
what are the protection components on HT Side and LT side?
what is the difference between thyristors and capacitors
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)