Answer / sandep
load is depend on p.f.
say pf=1 then load is=10kw and 25kw
for pf .9 then load is=9kw and 22.5kw
| Is This Answer Correct ? | 49 Yes | 10 No |
Answer / aruloli
Dear Friend
You forgot to furnish few more data i.e Voltage rating of
primary and secondary.
If i assume Voltage rating for 10 KVA Transformer as 230
V/110 V (Primary/secondary)and considering as single phase .
primary load current is calculated as
P=VI
10*1000(VA)=230*I
I=43.47 A
Secondary current is ,
90.90 A
Considering Transformer as 3 phase, then
P=1.732*v*I
Primary load current is
10000=1.732*230*I
I=25.10 A
Secondary is,
52.48 A
| Is This Answer Correct ? | 35 Yes | 15 No |
Answer / k.sri405
10 kva & 20 kva means transformer apparent power that is
combination of active and reactive power so we can load this
transformer below its rating coz load means only active
power .but in case of purely resistive losd we can load this
transformer upto its rating but practically purely resistive
load is not possible.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kaleem
aroluli which voltage we'll use ? line to line to line to line to ground ?? 230 or 400 this formula to calculate 3 phase current ?? p= 1.73 v i cos@
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / dkverma67
For 3phase transformer
10 KVA=10*1.4 Amp=10.4 Amps maximum
25 KVA=25*1.4 Amp=35.0 Amp max.
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / pillay
the max load you already said as 10 kva and 20 kva. In terms
of kw it will be 10 & 2o kw also, so long it does not exceed
10 & 20 kva ampere ratings.
| Is This Answer Correct ? | 5 Yes | 6 No |
Why do we require transformer with less specific weight if supply frequency is increased?
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem
wat s the electronic device used in the fan regulators recently?
solar cell voltage?
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
A heater capacity is 3.0 KW on 415V . if supply voltage is 380Volt . what is heater capacity on 380volt . and how calculate and give formulas . Prakash veer singh Roto power Engg.
what is surge impedance loading and it's significant in power system?
how much flux density of CRNO core
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
What is use of starter and choke in tube light
what is static excitation and dynamic excitation of synchronous generator,scr excitation is a brush or brushless excitation?
ell me capacitor bank chossen formula.load in KW
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)