how to calculate a cable size while load is given in amp or
kw and length is also define.?
Answer / karteek.k
there is an empirical formula to calculate voltage drop for
given cable, when you are given load in amps, i.e
(1.732x1.1xIxLxR)/1000.
1.732- square root of 3(because 3 phase circuit)
1.1- multiplication factor
I- load current in amps
L- length of the cablertee
R/1000 - resistance per kilometer
if u get voltage drop below 5% of the given voltage, i.e
415V, it will be optimum to use that cable otherwise we need
to go for next higher rating.
Is This Answer Correct ? | 9 Yes | 0 No |
As the one point of eac phase winding is connected to each other in satr connction. Even if that at distribution side collesion of two diff phases result in to blast. Why?
dear all, How do i increase UPS (1000VA)backup time ? i have connected 2 12v wold you please 120 aH battery externally. ups charge the lead acid battery only 12.7 volt. backup time only 10.00 minuts and gose off. can any one of you help me?
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
srij i need the relationship b/w KW AND KWH and with an electrical example. plz send if u can?
Why the colour of insulator is always is chocolate in colour?
what is reactive and active power?why we need power factor correction?
Why power factor does not occur in DG set ?
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
why the oscillator doent need the ac voltage??how can it produce the ac voltage by applying the dc voltage only??
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64