what is the diff of mcb and mccb
Answers were Sorted based on User's Feedback
Answer / desingurajan
MCBs are miniature circuit breakers with optimum protection facilities of overcurrent only.These are manufactured for fault level of up to 10KA only with operating current range of 0.5 to 63 Amps (the ranges are fixed), single,double and three pole verson.These are used for smaller loads -electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection facilities of overcurrent, earth fault.it has a variable range of 50% to 100% operating current.They can be wired for remote as well as local operation both.They are manufactured for fault levels of 16KA to 50KA and operating current range of 25A to 630Amps.They are used for aplication related with larger power flow requirement.
Desingh
RAjapalayam
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / kadher.304
mcb its thermal operated and use for short circit rating of
mcb 63amp(max)
mccb is thermal operated for over load current and magnetic
oprataion for instant trip in short circuit condition.rating
of 63amp(9min)
| Is This Answer Correct ? | 7 Yes | 1 No |
DC Motors applications used in Lift/Elevators
8 Answers IOCL, SCS, Usha Martin,
why bulbs when connected in series glow dim
my motor rating is 800HP, 128Amps, 3.3kV. What is capaitor bank i can use for PF improvement to 0.990?
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)
Plugging is a phenomenon to= A braking the motor B to accelerate the motor C to run IM as generator D to start the motor
What is purpose of reactor?.What is different between line and bus reactor?
why should a transformer be never connected to dc supply
What is the permissable nutral current of three phase system as per IS standards?
In the Variable Voltage Variable Frequency Drive, how the Voltage and Frequency varied ? Is it varied in the Inverter part of the Drive ? Please give us supporting document if any.
how to calculate slip ring induction motor stator and rotor currents??
Which pump set is more suitable and economical for liftingwater from 300Mtr borewell? A. Compressor Pump B. Submersible Pump C. Jet Pumps D. 25HP Centrifugal Pump Q. from PSC Test 22-11-2008 Meter reader
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)