what is the diff of mcb and mccb
Answer Posted / desingurajan
MCBs are miniature circuit breakers with optimum protection facilities of overcurrent only.These are manufactured for fault level of up to 10KA only with operating current range of 0.5 to 63 Amps (the ranges are fixed), single,double and three pole verson.These are used for smaller loads -electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection facilities of overcurrent, earth fault.it has a variable range of 50% to 100% operating current.They can be wired for remote as well as local operation both.They are manufactured for fault levels of 16KA to 50KA and operating current range of 25A to 630Amps.They are used for aplication related with larger power flow requirement.
Desingh
RAjapalayam
| Is This Answer Correct ? | 16 Yes | 0 No |
Post New Answer View All Answers
What is difference between isolator and circuit breaker?
What is process of anneling transformer core
why three phase capacitor takes unbalanced current in capacitor bank?
Dear all: Recently we got a question about Interface between PMS and SAP-PM.once we got a update message from PMS.we should set the deletional flag for functional location in SAP system.Is there any FM or BAPI to use?There are only functional location create and change provided by SAP. Best regards!
why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??
what is harmonics? what are the factors it will depend upon
An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?
as a electrical student why should i hire you?
how does a liquid starter reduce the starting currents?
what is the responsibility of C license holder in industry?
Motor,transformers,capacitor tubelight etc....
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
i have total 8 dg sets for synchronizing and 2 buscoupler,1 sectoin dg no 1,2,3,and 2 sectoin dg no 4,5,6,and last section dg no 7,8 ....if buscupler no 1 and 2 is off mode ..than dg no 1,2,3,will synchroniz of another dg sets?