How the flow can be measured by using DP Transmitter?
Answers were Sorted based on User's Feedback
Answer / mobin ahmed sabayek
for flow measurment first need creat difrential pressur by
using of orific plat in flow path dp tranmitter have low
and high side cannect high pressure and cannect low side of
low presure of tapping and transmitter will convert
diffrential pressure in to 4 -20 ma
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ashish namdev, bina refinery [
A DP type transmitter senses DP pressure from LP & HP tapping.
after sensing DP we will have to change some settings in the
transmitter, the settings are as follows -
1. set the range in output block.
2. change display parameter from linear to square root.
3. change display unit as per your requirement.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / george mathews
When we are going to measure the flow using a DP
Transmitter there must b a Flow Instrument placed there. So
if we see the basic structure of a flow instrument we can
clearly see that one side the orifice is normal and it goes
on shrinking toards the other end like a conical shape.
so we connect the higher end of the dp to the normal
orifice and the lower side to the other end of the flow
instrument. and when there is a flow there ll alwyas a
difference in the pressure as soon the water/ oil / gas
enter the flow instrument the normal end is at high
pressure but the exit end is at lower pressure due to d
manufacture of the instrument. And we can get out
measurment .
| Is This Answer Correct ? | 1 Yes | 1 No |
what is difference between OP AMP and differential amplifier?
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
What are SMART insuments?
what does 5/2 solinoid valve means?
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz
why we use double acting valve and where?
how eddy current loss in probe and induced gap voltage accros probe trip and shaft
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
what is shutoff dp? why is it important for selection of a control valve?
What is surge in compressors? How to detect and control it?
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)