how will you calculate rated Primary and Secondary voltage and
Current for 2500 KVA, 11kv/443V Transformer
Answers were Sorted based on User's Feedback
Answer / rajutadhikari
Rated current on HV side:
Irhv = P/ (1.732 * V) = 2500k/ (1.732*11k) = 131.22 Amps
Rated current on LV side:
Irlv = P/ (1.732 * V) = 2500k/ (1.732*0.443k) = 3258.28 Amps
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / amit bose
primary I =(2500*1000)/(11*1000)
Secondary I= (2500*1000)/443
| Is This Answer Correct ? | 1 Yes | 3 No |
what is CT class? depending upon which it is classified?
where transformer is installed? a)generating station b)substation c)voltage regulating area
what is kvarh? Please define it With calculation General motors ?
What are the condition for parallel operation of transformers?
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
definition of fault level in powersystems?
what is the difference between metalhalide and mercury vapour lamp
electricity board have asked me what size meter i need fitted in my garage, its a 415volt supply and i want to run six 20amp supplies tolifts and things plus ten florry lights , what kva meter do i need??
Do you know the overhauling of a motor?
in a dc motor we supply current only to the armature conductors,from where is the field winding gets excited then??
why the under of transformer platform is filled with rock stones.
10 Answers TNEB Tamil Nadu Electricity Board,
What is GNR ? How much value of ground neutral resistance?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)