what is %impedanece
Answers were Sorted based on User's Feedback
percentage impedance is voltage drop on full load due to
winding resistance and leakage reactance
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sangeetha.np
The percentage represents the amount of normal rated
primary voltage which must be applied to the transformer to
produce full rated load current when the secondary winding
is short circuited. The maximum short circuit current that
can be obtained from the output of the transformer is
limited by the impedance of the transformer and is
determined by the multiplying the reciprocal of the
impedance timed the full load current . Thus, if a
transformer has 5% impedance, the reciprocal of .05 is 20
and maximum short circuit current is 20 times the full load
current.
Is This Answer Correct ? | 4 Yes | 2 No |
as we see that in our country the power rating for transmission is always rated in multiple of 11 like 11kv,33kv,66kv132kv. So i want to know wht is reason or logic here.
explain why the armature voltage changes when the field rheostat is varied in self excited DC generator
What is MODBUS Controller Used for BMS Mointoring???
I want formula to calculate current loss with distance in km.I searched many sites but didn't right answer.Plz reply me
why DG rating in kva
Why electric traction is used ??
Why heat produce in AC machine higher than DC machine?
why is it that the HT motors & motors having very low kW rating(<1kW) have windings connected in STAR, whereas the motors having in between kW ratings have DELTA connected windings??
in railways why we use the power in 10,20 30kv,why not in the multiple of 11kv
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
What are the basic elements used for modeling mechanical rotational system?
how much speed will trawiling current