why the SCAN time of DCS is more & that of PLC is less?
if the SCAN time of DCS then why we use DCS.
Answers were Sorted based on User's Feedback
Answer / bm
Scan time of DCS is more than the scan time of PLC when the
I/O's are digital.
Whereas the scan time of DCS is less than the scan time of
PLC when the I/O's are analog.
Hence DCS is better when analog signals are considered
whereas PLC is better when digital signals are considered.
However DCS do handle both analog and digital signals. It
can also have more no. of I/O's compared to PLC. Hence we
use DCS.
| Is This Answer Correct ? | 33 Yes | 7 No |
Answer / kyle condran
DCS are not PC based. the configuration and operating software are but the actual control happens in a control module. DCS usually have a fixed scan time 50ms+, but not always, regardless of I/O count or program size.
PLC scan time depends on Program size and I/O used in the program.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / solomon
Eventhough PLC scan time is less,DCS is selected for its
I/O availability.About 1 lakh I/O available in DCS.
| Is This Answer Correct ? | 11 Yes | 10 No |
DCS is pc based system. The speed of the processor/CPU
decides the scan time.
| Is This Answer Correct ? | 3 Yes | 28 No |
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
i have been asked by QAFCO to appear for interview for thy post of Instrument Designer(INTOOLS)..i m engineering graduate with 5 years exp. in design engineering.Will this job profile suit me??i need all ur help n suggestions for thy same?
Why do we go for 4-20mA? why not other standara?
what are the on/off valve precaution?
how to measured k type thermocouple temp.
What is difference between Ionization heat and bimetallic heat
What is re-latch the manual trigger in solenoid valve
0 Answers Valvitalia Systems Division,
Boiler flame scanner advantage?
0 Answers Fluke, Petrochemicals, Tata Chemicals,
what is droop in governer ,type of droop ,how it work
how to given power supply of any type two wire transmitter in field?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)