Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How can I zero check of wet leg type DP Tx ?

Answers were Sorted based on User's Feedback



How can I zero check of wet leg type DP Tx ?..

Answer / yasir nazir

if the transmitter is installed below the tank,then we have
to calculate the HP side level below the tank zero level,and
applying
that much pressure on HP side to check the zero level.

And if transmitter is installed at zero tank level,then
isolating the HP side and draining the HP side gives the
zero level at transmitter.

Is This Answer Correct ?    9 Yes 1 No

How can I zero check of wet leg type DP Tx ?..

Answer / manish dave

First isolate HP side of Tx. and open vent port of HP side.
LP Side fill service liquid up to LP tapping and set the
zero.

In this case your HP & LP both sensor working or not it was
clearly identified.
While applying span pressure on LP side in this case if HP
side sensor fails than transmitter will not work after zero
checking.

Is This Answer Correct ?    14 Yes 7 No

How can I zero check of wet leg type DP Tx ?..

Answer / gnanvendan

close HP line isolation valve and drain in transmitter,then
check the LP side pressure according to LRV whether its
same or not.

Is This Answer Correct ?    6 Yes 1 No

How can I zero check of wet leg type DP Tx ?..

Answer / praveen kumar

Close both the isolation valves of Transmitter, and open
the line vent in LP side

Is This Answer Correct ?    8 Yes 5 No

How can I zero check of wet leg type DP Tx ?..

Answer / manish dave

yes dear

First u knew range of transmitter then apply span at LP side

Is This Answer Correct ?    9 Yes 11 No

How can I zero check of wet leg type DP Tx ?..

Answer / id10t

Open bypass so HP=LP.

Is This Answer Correct ?    7 Yes 12 No

Post New Answer

More Instrumentation Interview Questions

In control valves (like feed water control valve) we will give 3 kg pressure and how it controls 110 kg of water pressure?

4 Answers   SSL,


How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?

0 Answers   CCIE,


How can we check Zero of DP type Level Transmitter onside?

7 Answers   Birla,


Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please

1 Answers   Shell,


need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate

0 Answers  


WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??

2 Answers   IOCL,


What is expansion of SMART Instruments? And What is it?

35 Answers   Atesco,


what is the Analog signal and what is the Digital signal

4 Answers  


1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling

0 Answers   BARC,


What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?

1 Answers  


why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V

0 Answers   Hospira,


How does the "as-built" function benefit plant owner/operators?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)