How to calibrate DP transmitter by using HART communicator ?
Answer / sunilkumar tailor
Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.
*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
Note:
Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.
| Is This Answer Correct ? | 5 Yes | 0 No |
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
Define all the process Variable and state their unit of measurement. ?
How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.
I am going to attend a recruitment drive by Schneider in 2 weeks. They have a technical test in the beginning. I would like to know what are the areas i should concentrate on while preparing for the test. My major is Electronics and Instrumentation.
What is furnace draft control?
Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?
what is pyrometer? which purpose it has to be used?
In E&I diagram what is the meaning of rectangular box and circular box
In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?
1 Answers Process Control Technologies,
Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?
How will you select suitable Instrument for Process line/Tank/Vessel?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)