Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calibrate DP transmitter by using HART communicator ?



How to calibrate DP transmitter by using HART communicator ?..

Answer / sunilkumar tailor

Step:
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.




*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
WARNING – If the process is hazardous, please unsure proper flushing is done to remove the entire hazard.
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*In this condition both capillary flange will be atm pressure at difference high
* Multimeter should show 4mA and PV at HART communicator should shows 0 (LRV)
*If not, do zero adjustment at transmitter using HART Communicator
*Connect pressure calibrator to high side flange (drip ring)
*Apply pressure depend data sheet span (URV)
*Multimeter should show 20mA and PV at HART communicator should shows same with URV
*If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.
















Note: 




Capillary flange at same elevation
Example calculation:
Transmitter range = 0-2 kg/cm2
LRV = 0 kg/cm2
URV = 2 kg/cm2.

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

when i installed Allen_bradley_RsLogix_500_Pro_V_7.0,after installation it gives the fatal error.it need activation file.from where and how i can find its activation file.

6 Answers  


principle of automatic votage regulator

0 Answers   Bhel,


how bolometer is used in temperature measurement ??

1 Answers  


What are the questions asked in fresher instrumentation candidates

0 Answers   Polmon,


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


In which principles tx ,pressure gauge,Temp gauge,control valve works?

0 Answers   Bajaj, Professional Instruments,


What is Process portal A(PPA)?

1 Answers   ABB,


What are different types of valves?

0 Answers  


there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.

4 Answers   GATE,


what is meant by orderm of a system. will the stability of a system increases by incresing order of a system

1 Answers  


1- Explain about HPM 2- What is the FSC and explain the configuration of FSC 3- explain the complete loop of vibration, how it works (field to control room) 4- What is the use of proxymitter? 5- During job your partner effected with H2S then what you have to do. 6- what type of gland packing uses when valve glind is leaking.

0 Answers  


My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)