Can DP transmitter with orifice plate works on Beta ratio
0f 0.3 and differential pressure of 100 MMWC in liquid
service application?
Answer / carl_ellis
An orifice plate (OP) creates a pressure drop in the flow
stream.
The question is whether an orifice plate 'works'. Works how?
An orifice plate will always 'work' by creating a pressure
drop; the proper questions are whether the permanent
pressure loss is excessive, whether the orifice plate has
been 'sized' for a specific medium at correct design
conditions, and whether the pressure drop (DP) is adequate
for instrumentation that senses the DP.
Orifice plates typically drop 100 inches water column at
100% flow rate, about 25 times the DP of 100mm water column.
A DP of 100mm water column at 100% flow rate is more
typical of an averaging pitot tube than an orifice plate. A
full scale flow rate of 100mm w.c. requires a low range
pressure transmitter, or one with a high turndown ratio.
A 0.3 Beta is acceptable.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
In turbine, what does term CDP, NI, NH, HSSOC, means
Senior engineer's please help me, what is Loop Checking and Loop test? and write difference also? soon urgent
what is all types of analyzer in water production plant?
which is type of thermocouple is used to measure 1000deg?
what is the difference about HART, and 4-20mA signal?
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
In most process, speed of motor controlled by control system with a reference pot . Now if i start & it becomes uncontrollable, i.e.gets directly start & stop after certain time.Then which reasons can make such problem? can motor may be faulty?how?
Which Signal hart communicator work? If there any signal change when hart connect while transmitter in line ?
Types of contol loops
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Explain the working of an enraf level gauge.
What is close loop ?
1 Answers College School Exams Tests, GMR,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)