Can DP transmitter with orifice plate works on Beta ratio
0f 0.3 and differential pressure of 100 MMWC in liquid
service application?
Answer / carl_ellis
An orifice plate (OP) creates a pressure drop in the flow
stream.
The question is whether an orifice plate 'works'. Works how?
An orifice plate will always 'work' by creating a pressure
drop; the proper questions are whether the permanent
pressure loss is excessive, whether the orifice plate has
been 'sized' for a specific medium at correct design
conditions, and whether the pressure drop (DP) is adequate
for instrumentation that senses the DP.
Orifice plates typically drop 100 inches water column at
100% flow rate, about 25 times the DP of 100mm water column.
A DP of 100mm water column at 100% flow rate is more
typical of an averaging pitot tube than an orifice plate. A
full scale flow rate of 100mm w.c. requires a low range
pressure transmitter, or one with a high turndown ratio.
A 0.3 Beta is acceptable.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
What should be hight of CONTROL panel for access & OPERATION What is BIS & INDIAN STD for SAME?
in a power plant which system are compensated?
dear friends, i have seen flow as the selection critriea in presure guage (bourdon tube) and i would like to know what is the relation between flow and performance of pressure guage other parameters i found in the data sheet are pressure max. 1ksc temperature max. - 50 deg c line size - 80NB operating range - 1ksc pr. guage range - 0-2 ksc thank u,
What is the formula to convert mv to temperature in k type thermocouple?pls simply elaborate? I got one ans.it is Temp=mv×25°+atmospheric temp,but here what is 25°,i confusef ,so pls????
typical loop drawing of a simple feedback control comprising of one transmitter and one control
why the derivative in PID is always set to zero?
difference between null and deflecting instrument.
i am working in the automation company...i want to just know how actully pid control valves are tune????...
How can one improve linearity of an RTD based temperature measurement system?
pls provide me syllabus and old question paper of instrumentation engineering for GET(JSPL)
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com
1 Answers Operational Energy Group, Process Control Technologies,