Answer / carl_ellis
An orifice plate (OP) creates a pressure drop in the flow
stream.
The question is whether an orifice plate 'works'. Works how?
An orifice plate will always 'work' by creating a pressure
drop; the proper questions are whether the permanent
pressure loss is excessive, whether the orifice plate has
been 'sized' for a specific medium at correct design
conditions, and whether the pressure drop (DP) is adequate
for instrumentation that senses the DP.
Orifice plates typically drop 100 inches water column at
100% flow rate, about 25 times the DP of 100mm water column.
A DP of 100mm water column at 100% flow rate is more
typical of an averaging pitot tube than an orifice plate. A
full scale flow rate of 100mm w.c. requires a low range
pressure transmitter, or one with a high turndown ratio.
A 0.3 Beta is acceptable.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
how to convert bar to mA?
i want to control the temp of sand(welding flux) between the range of 150deg C to 170deg C. sugges me sum temp control method without PID controller.
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)
What are different types of cable?
Manipulation of dead wt. tester double piston type.
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
What are the Components of Siemens S7 300 Series PLC system ?
how to define the P,I,D value in tuning pid loops in online.
Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?
how can we calibrate the differential pressure transmitter by using HART communicator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)