length of 4 core cable 95mm from substation LV VFD panel to
Motor at field approximately 150 meter. Motor stop and power
has been isolated from LV MCC ( Substation )to disconnect
Motor for services. After Motor completed service propose to
reinstall and reconnect Motor Cable, found earth cable
sparkling during touching at metal / motor body.
Inspect by clamp meter found earth cable have current flow
AC 1-2amps and all earth cable at MCC LV also have current
flow as same value. why it is happen?
Answers were Sorted based on User's Feedback
Answer / elavarasan.p
in sub station Hv side side leakage current will flow then
body earth will be samely to be connect to be in the lv
side some earth current will flow in lv side thats will be
approximately 1-2A will flow
| Is This Answer Correct ? | 2 Yes | 2 No |
Cable insulation together with cable conductors form
capacitance. On nergising a cable this capacitance gets
charged and cable charging current flows even if no load is
connected at cable end. Similarly when cable is disconnected
from power source it retains the original charging energy
until it finds a conducting path to earth for discharge.
Hence before touching a disconnected cable all its
conductors including metal sheath and armours should be
connected to a earth path so that the stored energy in the
cable gets discharged.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is tranformer differtial?
The Q-facr o of a coil given as wL/R. what will be shape of Q versus frequency graph.
what is static excitation and dynamic excitation of synchronous generator,scr excitation is a brush or brushless excitation?
what is main reason for grid earthing for any industry
why universal motor work on ac & dc both?
why does voltage generation at 11 kv?
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB Machines of higher rating?
From the point of view of accuracy in the Measurement of Electrical energy should we select a potential transformer or a capacitor voltage transformers?.Kindly support your reply with reason and justification.
What should be the height of basement according to NBCC code?
what is the use of spherical metal balls attached on to the earth wire of transmission over head lines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)