what is working of Master trip relay ?
Answers were Sorted based on User's Feedback
Answer / guru
In a protection system due to large number of protection
relays provided for various types of faults, all the
tripping devices are connected to a master trip from where
the tripping command goes to the concerned circuit breaker.
Is This Answer Correct ? | 88 Yes | 9 No |
Answer / hirak subhra majumder
In Several sub-stations and power houses a special type of
installations is applied i.e. generally O/C relay for B and
R phase and Earth fault relay for Y phase. From there the
three trip connections are coming out and is connected to
the master trip coil. Now this relay output is connected to
the circuit breaker. Thus the other relays works here as
slave(Not mandatory) and the later one as master controlling
the operation of the circuit breaker.
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / a.n.v.kartik
Master trip relay is the relay used for which for any fault
on any electrical equipment got trips in addition to the
relay associated for that fault
Is This Answer Correct ? | 25 Yes | 13 No |
Answer / raviteja.n
In any substation master trip relay is employed bcz it
master relay and other relays act as slave relays. Any relay
may it be O.C ,REF, Earth fault relay,Buchloz relay etc.,
will sense the faulty nature of the circuit and they will a
signal to Master trip relay then master trip relay will give
tripping command to CB.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / pratik
Actually the master tripping relay is connected in
conjunction with all the abnormal conditions which are
probable to occur on the system & operates when any of the
concerned fault occurs & sending a tripping command to the
CB.In addition to this it also locks the closing circuit of
the CB so that if any personnel or external control circuit
if tries to close the CB,the CB won't close until the fault
is resolved & the relay is reset.
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / anbarasan
Master trip relay called multifunctional relay. Its analyze
power quality and fault conditions and protect power system.
This one purpose of isolating faulty power and make
continue operation in equipements(like DG and Main power
parallel opertaion). and its given analoge and digit and
communication outpus also its use for plant automation and
monitoring in closed process.
Is This Answer Correct ? | 10 Yes | 6 No |
Answer / neeraj vishwakarma
Basically master trip relay is called master coz it has the
least operating time ie;it trips first .also it works to
multiply no. of contacts..for eg.if Spam 150 C relay gives
trip contact to master trip relay ..the MTR trips with
changeover of contacts..you can use those contacts for
tripping breaker ,getting indications on DCS etc.
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / mahammad rafi
The tripping contacts of protection relay may not be
adequate to carry the current of tripping coil. Hence, a
seperate tripping relay is used to give tripping command to
the trip coil, called Master Trip Relay. The operating
element of the Master Trip Relay is energised through the
respective protection relay. Further, in the event of
provision of more than one number of protection relays, a
seperate relay called Master Trip Relay is provided to
receive the trip command which in turn trips the switch
gear.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / nagarjuna
Mater trip relay is one of the latch relay the ANSI Code is 86, It is working like Auxiliary relay but the additional feature it have when fault occurs it is trip after fault clear we need to reset Manually
Is This Answer Correct ? | 0 Yes | 0 No |
is there any current and voltage drop on liquid resistance starter water/soda tank ?
what is d meaning of inrush current of a trafo ? how u can calculate this ?
How to reduce power factor correction capacitors failure in an industrial environment with vsd and computers usage in the system
salam,hi, i need to know what the spesification of 300amp msb...
i need 24v dc from 230v ac supply how we can getit ? what are the devices &its rating requied for that ? plzz i need answer urgently .thank u
how much UPS neutral erath leakage current.
what is anode and cathode??
Where is the best place to mount distribution panel in a house.
0 Answers Wantro Technical Services,
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
what is the ka rating of mccb. and how it is decided .
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
how to protect motor in dol starter having capacity of 30 hp.40 hp?