HOW TO CALCULATE CT AND VT RATIO IN PRTECTION AND METERING?
Answer / naveen singh
To find out Multiflying factor
1) If meter CT Ratio is not given then CT Ratio provided in
the panel has to be considered. Example if CT Ratio in the
Metering Panel is 600/5 then the M.F is 120.
2) If CT Ratio is mentioned in the Meter then Meter CT
Ratio / CT Rating Provided in the Metering panel.
Example If the CT Ratio of the Meter is 600/5 and CT
Provided in the Panel 800 /5 then Multiplying Factor will
be 600/5 /800/5. i.e., 600/800 then M.F is 3/4 (0.75)
3)In addition to this any Multiflying factor is mentioned
in the Meter then it has to be multiplied. Example if Meter
CT Ratio is 600/5 and Panel Ratio is 800/5 and M.F
mentioned in the Meter is 3 then the M.F will be (600/800)
*3. i.e., 0.75*3 =2.25
Is This Answer Correct ? | 20 Yes | 8 No |
what is phase angle and how its generate moreever how we measure the phasse angle?
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
what is power?
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
if 20 hp motor starts directly stars and contenious run . what will be the effect.
11 Answers HP, Ohsung Electronics,
what is meant by fuzzy logic? what is fuzzification and defuzzification?
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
i alternator which of genarator used for excitor the what is reason?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
What is the physical significant of power factor?
What is meant by knee point voltage?