how can I check HT cable ?
Answers were Sorted based on User's Feedback
Answer / bivin shankar
by meggering the unlive cable by selecting the option 5kv
in megger and check the insulation resistance value between
the core and harmour and between cores.for the healthy
cable the insulation resistance value should be infinity.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / umesh bawa
we can check HT unlive cable with the help of megger.so in
this way we can check resistance of cable.To remove the
moisture of cable we can give LT line(440v).so in this way
we can remove the moisture.
Is This Answer Correct ? | 10 Yes | 3 No |
will we get shock from dc?
Why in ESP Positive earthed
as per IE stranded what is max voltage between neutral to earth. 100 kva transformer neutral solid earth. min and max values i need to ans for RTI question
What is the use device of the grid.
In which type of circuit short circuit is dangerous in parallel or series and why?
Dry type transformers
in a dc motor we supply current only to the armature conductors,from where is the field winding gets excited then??
how to select proper cable for ct wiring so that drop within the limit.
11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?
oil cooled transformer
what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.