What is the method to calculate the capacitor bank rating
for say 50 KW load and how do we connect each capacitor to
busbar??

Answers were Sorted based on User's Feedback



What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect..

Answer / amrinder

50 KW is 68 hp ,that means we have to connect three 22.5
KVAR capacitors in delta..?? Please Justify

Is This Answer Correct ?    6 Yes 0 No

What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect..

Answer / vijay kumar

Actually motors are designed at 0.8pf.
50kw load means 50/0.8 kva i.e to 62.5 kva
we know that kvar=kva*sin(angle b/w V & I)
To take Power factor to Unity we need Kvar=62.5*0.6
=37.5 kvar

Is This Answer Correct ?    4 Yes 3 No

What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect..

Answer / santoshvarma

Before connecting a capacitor bank we have to know for what
purpose we are connecting, if the load having power factor
of 0.8 and if you want to increase the power factor to 0.95,
for that you need to install capacitor bank. The rating of
the capacitor bank can be calculated as follows

Required KVAR rating of capacitor bank = KW(of
load)*(tan(cosinver 0.8)-tan(cosinve0.95)

By this way you will get the kvar rating of capacitor bank.

The capacitor is always connected in parallel to load bus.

Is This Answer Correct ?    2 Yes 2 No

What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect..

Answer / biswajit sahoo

generally hp/3,connected in delta

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

How Earthing is prevents shock?Explain

4 Answers  


What is bus-bar?

1 Answers  


What is the required bending radius requied at the time of cable laying?

1 Answers  


where we use zero sequence current transformer or core balancing ct.

2 Answers  


How can we convert 11 kv to 440 volt without using transformer ?

1 Answers   Electrical,


Is VVVFD reduced the starting current of an induction motor?

1 Answers  


what is the difference between relay, contactor

4 Answers   BRSS, Vishay Intertechnology,


To have variable speeds we use a. Induction motor b. Traction motor c. Shunt motor

1 Answers  


why synchronous motor has zero starting ?

8 Answers   NTPC,


what is AB switch???

6 Answers   NTPC, Simplex,


why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer

2 Answers   Bell, TCS,


what is anti-pumping relay and the significance of it in a switcgear cb control system?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)