What is the method to calculate the capacitor bank rating
for say 50 KW load and how do we connect each capacitor to
busbar??
Answers were Sorted based on User's Feedback
Answer / amrinder
50 KW is 68 hp ,that means we have to connect three 22.5
KVAR capacitors in delta..?? Please Justify
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vijay kumar
Actually motors are designed at 0.8pf.
50kw load means 50/0.8 kva i.e to 62.5 kva
we know that kvar=kva*sin(angle b/w V & I)
To take Power factor to Unity we need Kvar=62.5*0.6
=37.5 kvar
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / santoshvarma
Before connecting a capacitor bank we have to know for what
purpose we are connecting, if the load having power factor
of 0.8 and if you want to increase the power factor to 0.95,
for that you need to install capacitor bank. The rating of
the capacitor bank can be calculated as follows
Required KVAR rating of capacitor bank = KW(of
load)*(tan(cosinver 0.8)-tan(cosinve0.95)
By this way you will get the kvar rating of capacitor bank.
The capacitor is always connected in parallel to load bus.
| Is This Answer Correct ? | 2 Yes | 2 No |
What is bushing?
why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?
what is the meaning of 16/20 mva of transformer
WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON PRIMARY OR SECONDARY SIDE OF TRANSFORMER?
can we check the resistance of earthing electrode while it is connected with the neutral of UPS system
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
what are FM 200 systems? why it is useful for electrical systems ?
Is it a better option to procure screw type air compressor rather than reciprocating air compressor?If so, what is the reason?How should we select an air compressor(100 CFM)? Please mention the important parameters of air compressor.
Generally the incandescent lamps in bathrooms fuse due to high voltage at night.What is the simple solution of this problem?
1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.
what is breathing?
What is a doble test
1 Answers KPSC Karnataka Public Service Corporation,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)