where we use zero sequence current transformer or core
balancing ct.
Answers were Sorted based on User's Feedback
Answer / blake australia
To detect earth faults:
Zero sequence refers to the current flowing during an earth
fault. 2methods of decting earth fault.
-Measure the current on the earth return cable
-Measure the current imbalance on the 3x phase cables (do
this by putting all three through the same core balance CT.
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / prabhakar
For 51G protection we normally use the CBCT(Core balance
current transformer)for to detect the unbalance current
caused due to earth fault
Is This Answer Correct ? | 8 Yes | 3 No |
i need online ups battery calculater
why the altrnator(AVR) not showing the any voltage after making the new winding and insulation?
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
Why primary batteries not rechargeable and secondary batteries are rechargeble??? If any one know please send me.
what is the reason for earthing static equipments? why?
Will a bulb glow if we connect it between the phase and earth instead of earthed neutral?
can we install HT panel & LT panel side by side or how much clearance is required ?
Is it a better option to procure screw type air compressor rather than reciprocating air compressor?If so, what is the reason?How should we select an air compressor(100 CFM)? Please mention the important parameters of air compressor.
Whats meant by trivector meter where it is connected at the substation?
20 Answers GPIL, Infosys, Jakson, L&T, Secure Meters,
Witch do depand of Power factor and theory of power factor?
wat is the need of capacitor on aceiling fan?
why semicondoctor use in HT cable?