I can follow below trouble shooting steps,
check the error code to see if there was any short ckt or
earth fault, if there was (check for cable termination if
the connections are not burnt out due to short circuit,
check earth resistance and current voltage etc. of the
terminals) eliminate the fault then it should work fine.
Check the control wiring of the breaker check the fuses,
contactor operations etc.
check the under voltage release to see if it did not trip
due to under voltage or over voltage. check shunt trip
mechanism.
check if breaker is not overheated as a breaker may not
close if magneto thermal release is tripped.
check closing coil operation and see whether breaker gets
charged automatically with help of the motor.
if none of the above problem found, Rack out the
breaker(keep it in isolated position)trip the breaker
manually a few times and try closing it again should work fine.
In case it does not happen you can try and by pass the
breaker with help of crocodile pin Jumpers ( In case of
Emergency), but one need to be extremely careful and should
ensure that the incomer supply to breaker is turned off
while doing it, as a high risk is involved. Also you should
be confident that breaker did not trip due to an abnormal
condition.
Note: Some breakers indicate nuisance fault as well
Further,
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh arumugam
Please mention the voltage rating and the type of breaker i.e whether ACB or VCB or vcu
| Is This Answer Correct ? | 0 Yes | 0 No |
what is AVP?
Why the ceiling fan rotate in anticlock wise direction whereas tables fan rotates at clock wise direction?
what is IP65 & What is its advantages
how can we measure 220kv or more than these voltages ...?and also how can we conform whether we r getting 220kv from generating stations throuth the h v transmission lines?
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
what's transient & sub- transient reactance means?
I had finished D.E.E.E at 2004,I wish to take C license.I am working pvt company HT supply but my professional certificate was missing.I have diploma & course completed certificate.without professinel may I got c license?.pls guide me.
how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know that incoming cables for trnsformer
6 Answers Daikin, KOC, Reliance,
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requires ngr ?
What is the simplest formula to calculate the rotor diameter of a synchronous generator?
what is the use of tertiary winding?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)