If the circuit breaker will not close or it will trip, what
will you do?
Answers were Sorted based on User's Feedback
I can follow below trouble shooting steps,
check the error code to see if there was any short ckt or
earth fault, if there was (check for cable termination if
the connections are not burnt out due to short circuit,
check earth resistance and current voltage etc. of the
terminals) eliminate the fault then it should work fine.
Check the control wiring of the breaker check the fuses,
contactor operations etc.
check the under voltage release to see if it did not trip
due to under voltage or over voltage. check shunt trip
mechanism.
check if breaker is not overheated as a breaker may not
close if magneto thermal release is tripped.
check closing coil operation and see whether breaker gets
charged automatically with help of the motor.
if none of the above problem found, Rack out the
breaker(keep it in isolated position)trip the breaker
manually a few times and try closing it again should work fine.
In case it does not happen you can try and by pass the
breaker with help of crocodile pin Jumpers ( In case of
Emergency), but one need to be extremely careful and should
ensure that the incomer supply to breaker is turned off
while doing it, as a high risk is involved. Also you should
be confident that breaker did not trip due to an abnormal
condition.
Note: Some breakers indicate nuisance fault as well
Further,
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh arumugam
Please mention the voltage rating and the type of breaker i.e whether ACB or VCB or vcu
| Is This Answer Correct ? | 0 Yes | 0 No |
how many types of motor can be used in washing machine
difference between generator and alternator
What is the difference between Rectifier & Converter?
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
Please give me a erda placement paper
What is broken wire condition in transmission line?
what is servomechanism?
In a house wiring why we are using only one neutral wire and so many phase wires from the main board, when the load is common for both wires?
what will happen if ac motor given dc supply?
features of hbc fuses
What happens to voltage when current is zero?
10 hp motor ,7.5 kw ,960 rpm, full load current 15.5, delta connection so how much take current no load trial time. any formula please give..... second question :- what is different between brekar control wiring and motor starter control wiring
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)