How I design capacitor bank for different load.7MW
connected load.
Answers were Sorted based on User's Feedback
the capacitor bank depends on the load type
1. for resistive load no need cap.bank
2.and the cap.bank calculation depends on the Power factor
(for inductive loads 0.8 pf lag)
if u want clear calculation mail me with all load perticulars
mail id: viswaeee60@gmail.com
Is This Answer Correct ? | 3 Yes | 4 No |
the capacitor bank reqired almost 30 persent of full load
(kva) but exectly we must know the desired powerr factor
KVAR = kw/Sin theta
pf= cos theta= desired pf
let 0.99 we require than cos Q = 0.96
Q= Cos inv 0.96
SinQ Will = sin * Q
Kvar = Sin Q* Load
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / mior
First and foremost, you need to know what is your required
KVAr; then, you can design the capacitor bank to suit with
your required KVAr.
The purpose of designing the capacitor bank is to correct
the power factor to the desired value. By doing so, you can
reduce the loses of power as well as reducing your
electricity bill.
The link below might help you on how to design the power
factor correction and how to design the capacitor bank.
http://guide4electricalconsultant.com/power%20factor%
20correction.html
http://guide4electricalconsultant.com/design%20cap%
20bank.html
Is This Answer Correct ? | 1 Yes | 5 No |
What is Surge arrest? How it work?
how to calculate voltage regulation?
how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
3 Answers Megatron Solutions, TCS,
What is the Minimum winding resistance of motors ( small & big)? referance range
what are the protection for DG set and why?
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
why semicondoctor use in HT cable?
Application wise, where we should use AC motors and where we should DC motors?
what is the major difference between LIBBP & HIBBP.. which one is most preferable..
Hi Friend I am used multimeter to measure the voltage between R Phase(SS1) to R Phase(SS2). In SS1 is connected with UPS loads. But I am getting voltage between these 2 R Phases. Please give some idea friend
what is the basic differnce between ground and earth
what is the use of earthing ?