What is derating factor in Motor?
Answer / touch2gobi
Derating Factor value depends upon the motor environment,
For example:
Motor design temp – 45 deg C
But motor location ambient temp 65 deg C (near any burner
or heat source)
So motor performance (rated power) will reduced due to
ambient temp.
For that motor manufacturer given Derating Factor value.
Ex:
Rated power = 45 kW
Derated power = 42 kW (Operating Temp – 50 deg C)
Is This Answer Correct ? | 25 Yes | 19 No |
Why plc require in analog input 4-20amp & 0-10 volt?
send me HPCL paper
How to calibrate a orifice differential pressure flow transmitter in process?
Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?
What is PLC(programmable logic control)?
how micro-processor and micro controller different from architecture
3 Answers Bhushan Power Steel,
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
What is Modbus communication
why we use the 4-20 mamp signal used for transmitter.
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider