Answer / imran mansuri

For gas and vapor flows, it is important that
no stray liquid droplets collect in the impulse lines
leading to the transmitter, incase vertical liquid
column begin to collect in those lines and generate an
error-producing pressure For liquid flows, it is
important that no gas bubbles collect in the impulse lines,
or else those bubbles may displace liquid
from the lines and thereby cause unequal vertical liquid
columns, which would (again) generate an
error-producing differential pressure.
In order to let gravity do the work of preventing these
problems, we must locate the transmitter
above the pipe for gas flow applications and below the pipe
for liquid flow applications

Is This Answer Correct ?    5 Yes 0 No

Why the tapping connections are taking above for gas service and below for liquid service? ..

Answer / msn raju

Because gas want to went to atmosphere upside always and liquid always downside

Is This Answer Correct ?    4 Yes 0 No

Why the tapping connections are taking above for gas service and below for liquid service? ..

Answer / r.govindasamy

gas will not condensate so txr connected above fluid
line.Butsteam line steam will be condnsate.so txr connected
below fluid line.

Is This Answer Correct ?    2 Yes 0 No

Why the tapping connections are taking above for gas service and below for liquid service? ..

Answer / trideep

According to the charcter of gas in fluid mechanisam theary, it has no size and wont accumulate at the desired place/ tank if you say.. In case of liquid vice versa....

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

How to calibrate the flow transmitter

1 Answers  


When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?

2 Answers   Balco,


For an Instrumentation Engineer, is there any effect on Instruments of safety zones like zone0, zone1, zone2. As an instrumentation Engineer, what we have to consider or remember while working in these areas.( zones 0,1,2).

1 Answers  


hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank). can i use T/C or not?

10 Answers  


steam drum level transmitter calibration procedure? with example?

1 Answers  


How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?

2 Answers   QAFCO,


i want to know for good instrument engineer or success how many software knowledage required & from which university

0 Answers  


What is the DIfferences between SMART transmitters and PROFIBUS DP/PA Transmitters?

4 Answers  


what is the difference between transmitter and converters?

9 Answers   Videocon,


why relays are used with plc?

4 Answers  


How digital input and digital output 's are working in dcs

1 Answers   BBV, Indiabulls,


Example of dry contacts & wet contacts?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)