what are the standards used for earthing instruments in the
field?
The internal screen is always floating at the instrument.
This means we just put some heat shrink on it to seal it and
then tie it off inside the instrument and just let it lie
there. The overall screen (braiding surrounding the cable
just below the pvc outside)will be in contact with the gland
once you have installed the gland. On the gland thread you
install a copper gland ring and a red IP washer, and the
gland then are attached to the instrument. From the gland
ring you use a six mm bolt and nut with copper washers to
attached a small diameter earth wire (about 4 to 6mm is
fine). This earth wire is then attached to the outside of
the instrument at the earth connection point on it's
housing. Every instrument will have this earth connector on
the outside of it's housing. From there you attached another
earth wire to the earth boss nearby. This boss is normally
just a piece of round bar about 40mm in diameter and about
30mm long and tapped in the middle that is welded to the
structure close by, specially for this earthing of the
instruments. Again it is better to use copper washers. If no
boss is available you can use some other point on the
structure as well like a stainless steel cable tray for
instance but the earth boss should really be part of the design.
On the other side of the instrument cable at the RTU the
internal screen in attached the instrumentation clean earth.
The dirty earth is used only for electrical equipment.
Good luck
| Is This Answer Correct ? | 3 Yes | 0 No |
if we have 450 mm heigth boiler drum level ,so what is span & zero value for a dpt tranmitter
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
hello dear i have faced problem in drum level transmitter. the problem is when i engrize the meter meter shows 100% but the actual level 40 or something plz suggest me
How to Calibrate Vibration Probe (Axial, Redial) in field
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
hi vishok this is noor plz tell me what type problems will occured i use T/C in the place of RTD in (FEED WATER TANK),plz send ur e-mail address to my ID (mail2noor.hyd@gmail.com)
What are primary elements of measuring pressure?
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
in plc source and sink meaning?
what is meant by turn down ratio?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)