Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can
u give me Answer.

Answers were Sorted based on User's Feedback



How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / naren

connect to pressure calibator, apply the low pressure -60
adjust the span into low pressure and then apply the high
pressure then adjust the span screw into high value. it is
calibrated in the range of -60 to -20.

if it is the SMART transmitter its easy, just apply URV and
LRV value through Communicator then connect to the pressure
calibator then check URV, LRV and intermediate value

Is This Answer Correct ?    20 Yes 6 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / ramesh

we can apply the +ve pressure to the lp side that is 60
with zero, then +ve 20 with span with respect hp open to
atmosphere

or apply -ve pressure that is vaccum to the hp side with
respect lp open to atmosphere

Is This Answer Correct ?    10 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / welcome4ujd

make the calibration set up , to get -60 , give 60 in lp
sidethen adjust zero screw, give 20 in lp side toget -20
url , and adjust span screw.

Is This Answer Correct ?    18 Yes 12 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / sn

apply -60 to the transmitter n make the o/p as 3 psi, then
giv -20 as the input n adjust the o/p as 15 psi.

Is This Answer Correct ?    3 Yes 3 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / sandeep patel

connect transmitter in bench setup, left LP side of transmitter open to atmosphere and apply -60 mmwc to HP side and check it s o/p is 4 mA or not and if it is not, then do zero trimming. then apply -20 mmwc to HP side and check o/p is 20 mA or not otherwise fo span trimming.

Is This Answer Correct ?    0 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / suresh agravat 83204 78125

Urv-LRV÷4=Span
-60=4ma
-50=8ma
-40=12ma
-30=16ma
-20=20ma
Apply pressure accroding to above chart and monitor output

Is This Answer Correct ?    0 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / anup ramteke

It depends upon the type of transmitter u are having. If its
HART based transmitter then either u can calibrate it
through HART calibrator. firstly go to basic set-up mode and
feed the URV as well as LRV values. And if u want to
calibrate it at field itself when HART calibrator is not
available then u can set LRV value by entering its value in
mode 2 whereas for URV its mode 3.

Is This Answer Correct ?    2 Yes 4 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / suvendu sekhar giri

You can give positive pressure on low pr side keeping the
high side open to atomosphere for lrv (-60) & urv (-20)or
you can give negative pressure on high pr side for lrv(-60)
& urv(-20) keeping low side open to atomosphere.You can
adjust zero at lrv & span at urv. If it is smart
transmitter then you can zero trimming keeping both the low
& high pressure side open to atmosphere.

Is This Answer Correct ?    2 Yes 5 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / venkat

actually we can calibrate LP side by positive pressure and
Hp side also we can calibrate by negative pressure but LP
side better

Is This Answer Correct ?    3 Yes 7 No

Post New Answer

More Instrumentation Interview Questions

how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuring data communicate with plc system.

1 Answers  


In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.

0 Answers   India Cements,


How would you choose differential range?

0 Answers  


What is ultrasonic flowmeter?

0 Answers  


why does mA signal preferred for signal transmission?

12 Answers   Emerson,


Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?

0 Answers   AquaTech,


WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??

2 Answers   TATA, Tata Steel Limited,


Explain what is meant by the term “FLASH POINT” of liquid?

2 Answers  


what is a vortex flow meter,mass flow meter and electromagnetic flow meter.particular use of this.means in which condition particular meter is used.

0 Answers   L&T,


Can any body help to get Rsemulator 5000 free from internet if possible then give me any link or any help .

0 Answers   Engro,


what is the input of conductivity sensor and meter during the calibration time and what is the output?

2 Answers  


How will you select suitable Instrument for Process line/Tank/Vessel?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)