What is the correct procedure to shutdown VCB in 11kv
substation.safety and work procedure
Answers were Sorted based on User's Feedback
Answer / balaji
1. Preparation (Permit to work)
2. Separation (Trip the Breaker)
3. Isolation (Isolator isolates)
4. Earthing & Short circuit (Earthing)
5. Screening & Marking the area (Barricading the work area)
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / manzoor hussain
1)First need to obtain isolation permit(work permit)
2)Confirm substation no., breaker no.
3)Inform to control engineer
4)Transfer the load from LV side
5)First need to trip the vcb(electrically or manually)
6)Disconnect DS switch (isolator)
7)Need to close the earth switch (ES)
Is This Answer Correct ? | 0 Yes | 0 No |
What is the use of conservater, bucchos relay, breather in a transformer?
8 Answers Bosch, Wipro, Zadco,
control & auxilary circuits used for circuir breakers
How CT & PT ratings are decided for a 11KV or 33KV transmission line?
What is the minimum permissive IR value for LT & HT motor for safe starting?
How much sq,mm cable need for 800 amps load
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
what is the difference withbeen lighting capacitor and motor capacitor?
what is vector diagram in three phase transformer
What, in the construction of a transformer, controls KVA? For example 600/208/120 V transformer can be 10kVA or 45kVA!!! What do we change in the construction of a Transformer in order to change the rating but not the voltage.
What is the difference between LT & HT Cable
In electrical locomotive engines, the DC series motors is being used as traction motor. But in new engines like in WAP7 & WAG9 the 3-phase squiral cage induction motors has replaced them. So can someone tell me the advantages of induction motor over dc seris motor in engines points of view....???
11/.433KV, 100KVA TRANSFORMER is supplied with .433KV AT ITS PRIMARY. HOW MUCH KVA IT CAN SUPPLY