What is the correct procedure to shutdown VCB in 11kv
substation.safety and work procedure
Answers were Sorted based on User's Feedback
Answer / balaji
1. Preparation (Permit to work)
2. Separation (Trip the Breaker)
3. Isolation (Isolator isolates)
4. Earthing & Short circuit (Earthing)
5. Screening & Marking the area (Barricading the work area)
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / manzoor hussain
1)First need to obtain isolation permit(work permit)
2)Confirm substation no., breaker no.
3)Inform to control engineer
4)Transfer the load from LV side
5)First need to trip the vcb(electrically or manually)
6)Disconnect DS switch (isolator)
7)Need to close the earth switch (ES)
| Is This Answer Correct ? | 0 Yes | 0 No |
What is meant by TAN-DELTA test carried out in motors?
MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?
why the protection turbo generators is most complex?
what r the types of transmission line?
28 Answers DIET, RRB, WAPDA Water and Power Development Authority,
how to calculate P.F from kva only?
why ct mensioned 0.5/5p20 plese any reply to me
what is the working of air drayar
why voltages are multiple of 11 or 1.1???describe with derivation plzzz.thanks
Given a ckt,the max power dissipated in the load ZL ?
what is the difference between EMF and potential difference??
what are the duties of commutator in motor and generator?
what is ten delta test? what is the significanse of it
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)