Answer / ramesh kumar k
Mainly the current Transformer works on the principle that
Primary mmf = secondary mmf
i.e
Primary AmpereTurns(AT) = Secondary AT
so if the secondary is Open circuited, there is no current
in the Secondary hence secondary AT=0. In that case there
is no opposing mmf in the secondary to neutralize the
primary mmf. So the CT secondary will induce heavy
voltages and winding of the secondary will burn...
simply to understand guess what happends if we pump water
into a tank without opening valves for water to go out..
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / gulshan goyal
the mmf developed in the primary side will depend only on
load current which is highdue to which there will be high
flux in secondary also hence if we open circuit the
secondary the current present in sec will be zero,a very
high voltage will be generated which cause hazard.
| Is This Answer Correct ? | 3 Yes | 1 No |
How to select cable the size, what is the parameters use and what is the formulas use for this cable size calculation?
IN THE CASE OF AN ELCB, IF THERE IS ANY UNSTABILITY BETWEEN PHASE AND NEUTRAL IT MAY TRIP. BUT MY QUESTION IS WHEN A LOAD IS CONNECTED IN BETWEEN P AND N, THE LOAD CONSUMES SOME POWER AND THERE IS A DIFFERENCE IN NEUTRAL WITH RESPECT TO THE PHASE. THUS ACCORDING TO ME, THE ELCB WILL AUTOMATICALLY OPERATES WHEN EVER THE LOAD CONSUMES-- I KNOW IT IS WRONG. BUT THE SOLUTION IS?????????
i want to put single phase load on scott connected transformer,eventhough how to balance the transformer.
What will be happend if we not ground CT secondary?
3 Answers Enercon, Engro, THDC,
What is the difference between rulling span and wind span of of an Over Head Transmission Line?
5MVA TRANSFORMER SUDDENLY FAIL WITH THE PRV TRIPPING AND LARGE AMOUNT OF OIL SPREAD OUT? SO IT CAME BACK WITH THE REPAIRING WITH REASON THAT IT FAILS BCOZ OF TRANSIENT EFFECT? SO PLZ EXPLAIN HOW DOES IT HAPPENED?
what does mean of RCT and STR in diffrential CT?
hi sir i have load of 17.5kw in 3 phase lighting circuit which mcb i can use
While starting a high capacity motor, it takes 6 times the full load current. Why it doesn't trip relay or CB's in that network?
Define cuttoff frequency?
WHAT HAPPEN WHEN A DROP OF WATER MIXED UP WITH TRANSFORMER OIL ?
If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)