How to protect the water pump by no load running.
Answers were Sorted based on User's Feedback
Answer / prakash
If your concerns with domestic water pump dry run control,
then you can use a floating switch at level point that can
be connected to series with DOL starter if already installed.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jimmy
Just put level switch NC contact in series with overload
contacts in the Starter Circuit.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kamal
By using under current relay , setting is no load current,
below this level it trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth belani
We can protect a pump from no load running by using a
minimum recirculation line. This line connects outlet with
the main tank or the inlet. so there will always be some
minimum flow through the pump.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sandip paithankar
put a moisture sensor in land which need to wet on starting and ending point of it.then give to transistor then micro controller do if else program and understand the condition of land it may wet or dry.then give command to relay to operate the water pump
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ks
by using the level transmitter and with out plc with some
no nc additional elements in the contactor it is possible
to control.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / subrat.das1985
i think we can over come from this problem by using proximity sensor.or by using timer .
| Is This Answer Correct ? | 0 Yes | 3 No |
which %age if losses increases when frequency is increased to 25%
4 Answers Maihar Cement, Siemens,
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
Why two nos. un-tensioned wires are placed inside the PSC poles used by powergrid in RGGVY works.
how we can save electrical energy in industries,please give some inputs
Why star delta starter is preferred with induction motor?
What is the capacitance values of 132,220,400 & 765 kV current transformer
after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..
Why you want to join non technical field when you are an engineer?
what is skin effect? why is it absentin dc system
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
where the protection CT in neutral of transformer be located, before bifurcation or after bifurcation and why.
when we use neutral line as grounding.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)