How to protect the water pump by no load running.
Answers were Sorted based on User's Feedback
Answer / prakash
If your concerns with domestic water pump dry run control,
then you can use a floating switch at level point that can
be connected to series with DOL starter if already installed.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jimmy
Just put level switch NC contact in series with overload
contacts in the Starter Circuit.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kamal
By using under current relay , setting is no load current,
below this level it trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth belani
We can protect a pump from no load running by using a
minimum recirculation line. This line connects outlet with
the main tank or the inlet. so there will always be some
minimum flow through the pump.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sandip paithankar
put a moisture sensor in land which need to wet on starting and ending point of it.then give to transistor then micro controller do if else program and understand the condition of land it may wet or dry.then give command to relay to operate the water pump
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ks
by using the level transmitter and with out plc with some
no nc additional elements in the contactor it is possible
to control.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / subrat.das1985
i think we can over come from this problem by using proximity sensor.or by using timer .
| Is This Answer Correct ? | 0 Yes | 3 No |
clarify types of motor operated valves and advantages
why the motor running in delta connection ? it can be in star?
what is the difference between surge arrestor and lightning arrestor ?
what is the purpose for open delta connection in potential transformer
can i connect REF and Differencial relay in 1 CT core for transformer protection?
When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?
Star Delta Diagram with full description
0 Answers SKS Microfinance, Syscom,
what is the meaning of ceiling voltage in Generator exciter?
why high speed tripping relay is used in protection circuit why not normal relay
hi i am aziz electrical associate engineer. i am faceing problem in acs800 vvvf drive.it is tripping wothout any alarm/fault.i cheaked all parameters and fault function of drive, all are correct as well as communication parameters.but still it is tripping (drive is tripping in running position not in starting)
different aspects of voltage stability
What is UPS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)