What are the protections to be used for Generator?
Answers were Sorted based on User's Feedback
Answer / nishad
for the protection of generator we useing
1, under voltage/ overvoltage Relay
2Under/over frequency,
3, Reverse power relay,
4, Earth fault Relay
5, Differential Protection relay
6, over load protection
8, resticted earth fault relay ***(optional)
9,RTD's for bearing & winding >> protect from over heat
10,if it contain in clossed container provide differential
pressure relay,
These are the normal protection from Electrical side.
| Is This Answer Correct ? | 14 Yes | 0 No |
The following are the main protection schemes adopted for
our generator.
1. Generator Differential Protection
2. Generator & Transformer Differential Protection
3. Loss of Field or Loss of Excitation Protection
4. Negative Sequence or Current Unbalance Protection
5. Over Fluxing or Over Excitation Protection
6. Over Current Protection
7. Stator Earth Fault Protection
8. Rotor Earth Fault Protection (64R)
9. Restricted Earth Fault Protection
10. Backup Impedance Protection
11. Low Forward Power Protection
12. Reverse Power Protection
13. Pole Slip Protection
14. Pole Discrepancy Protection
15. Local Breaker Back Protection
16. Bus Bar Protection
17. Over Frequency Protection
18. Under Frequency Protection
19. Over Voltage Protection
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / renjith v.r
The following are to be used
1.Voltage restraint O/C relay
2. E/F relay
3. stand by E/F relay using CT in neutral earthing conductor
4. Under voltage ,over voltage relay
5. Differential potential relay
6.negative sequence relay
7.Vector surge relay
8.Reverse power and Reverse reactive power relay
9.rotor E/F relay
9.High vibration, oil temperature, Overspeeed and under speed alarm trip
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vedprakash uppadhaya
reactors, thyristor contoroled rectifier
| Is This Answer Correct ? | 2 Yes | 3 No |
What is the out put of a CT? How the ratio is decided ?
why the neutral point of star connnection oscillates?
which motor gives constant speed?
DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help
Difference between EDO and MDO breakers?
Why is the electric shock from the DC supply is more dangerous than the shock from AC supply.
if the armature current in a dc generator is ac ( sinusoidal ) why doesnt the sjhape af armature mmf a sinusoidal (ni) ? armature mmf in case of a dc machine is triangular.
difference between ac and dc generators
what will be the min and max voltage flow from neutral to earth?
Why use only DC supply to charge batteries why not AC Supply??
what is stray loss in transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)