How to determine earth fault level to set relay for a
normal distribution system of 11 kV , 100 A load????????
Answer / k.prakashchandra
EFR is usually set at 20 % of OCR.The earth fault current
is V/ Z of the line + ER value of the support.But you can
not expect this calculated earth fault current.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the difference between Rectifier & Converter?
can we increase our frequency rate in INDIA?
what is positive,negative and zero sequence in power system?
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
what is the use of CurrentTransformer in AVR ?
how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....
what is smart grid? why we use it? explain in detals bcoz i want give presentatin from it....
In which working principal temperature transmitter work.explain in detailed.
can you give me some names of projects which can be used in our daily life & which is having medium cost?
WHy neutral to ground trips when neutral touches the ground
how many types control panel of a 132/33 kv substation
Which system is best for industries 3ph 3w or 3ph 4w?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)