How to determine earth fault level to set relay for a
normal distribution system of 11 kV , 100 A load????????
Answer / k.prakashchandra
EFR is usually set at 20 % of OCR.The earth fault current
is V/ Z of the line + ER value of the support.But you can
not expect this calculated earth fault current.
Is This Answer Correct ? | 1 Yes | 1 No |