What is the unit of inertia constant of rotating machines?
Which has more inertia constant between turboalternator and
hydroaltermanor and why?
Answer Posted / iamdon
Inertia constant has unit of second(joule/VA).
Turboalternator has higher inertia constant in the range of
3-9 sec where as hydro alternator has inertia constant of 2
sec.
This variation is because in the case of turbo alternators
more then one(3 to 4) stages are connected to obtain high
mechanical input to alternator.Each stage has high rotating
mass.So more inertia constant.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 6 Yes | 7 No |
Post New Answer View All Answers
give some advantages and disadvantages of combiniing the session, presentation, and application layer in the osi model into one single application layer in the internet model
can we install HT panel & LT panel side by side or how much clearance is required ?
why magnetising curve not start with zero voltage?
what maximum range of star & delta in hp or kw ?
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
What is depreciation factor?
How the capacitance og capacitor volatage transformer is decided?
The simple way of finding the leakage quantity and % in compressed air distribution system
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
Why the frequency of ac in india is 50 hz but in some other countries it is 60 hz.
what is is the potential diffrence between two phase ?
I have a current transformer with 1 main reading meter with transformer outside the building and a control panel having 5 CT reading meters with black round coils inside the building. I want to know, A) when current pass through the Transformers, will the current be reduced or be the same and after that B) when current pass through the CT meters with black round coils, will the current be reduced or be the same. C) in the above process will the reading of the main meter be same or different, from the total reading of all the 5 CT meters.
Can u Explain about the electronic trivector meter and the use of data converters in them?