How the oil level of the Buchholz Relay come down.
Answers were Sorted based on User's Feedback
Answer / sajid hussain
When load increase on the secondary side of the
transformer,heat produced which decompose the oil i.e
hydrogen and carbon. This lightly Hydrogen gas entered in the
Relay Dom and produced pressure on oil at the upper side. The
oil level of relay housing decrease.If the heat produced is
too higher due to current flow or arc the decomposition of
oil is also high which cause the more oil level down in the
relay housing.
Note Any correction please send email
msajid1980yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / guest
The Buchholz relay functions by making use of the liberated
gas inside the transformer due to an internal fault, to
actuate an alarm or trip the circuit breaker depending on
the seriousness of the fault. The virtue of buchholz relay
is that it detects an incipient fault i.e in the very early
stage itself before serious damage is done, whereas others
relays operate after the fault has occurred. Therefore
repair measures are simpler. Example of incipient faults are
short circuited core laminations, broken down core bolt
insulation, failure of inter turn insulation and consequent
local over heating , bad switch contacts and faulty joints etc..
The relay comprises a cast iron housing inserted in the pipe
connecting the transformer tank with the conservator tank.
It consists of two bucket mechanisms each connected to a
tilting head on which a mercury switch is mounted. The upper
assembly , traps small gas bubbles generated by an incipient
fault and if sufficient gas has been collected, it closes a
contact and sounds a hooter in the control panel in the
SUBSTATION. The lower assembly which is directly in the path
of the connecting pipe operates when there is a serious
internal fault like a short circuit between phases , coils
or turns, earth fault, arcing or puncturing of bushing
insulator inside the tank. This liberates a considerable
amount of gas, and the displaced oil and gas surge through
the connecting pipe, and impinge upon a deflection plate
fixed on the lower assembly in line with pipe. This tilts
the Mercury switch which in line with the pipe. This tilts
the Mercury switch which in turn trips the circuit breakers.
The buchholz relay also detects accumulation of air on
account of low oil level, or faulty oil pumps. A per cock is
provided on the top of the housing to draw samples of
accumulated gas for analysis. An inspection window shows the
amount of gas which has accumulated. Provision is made for
manual operation on the alarm and tripping mechanisms to
facilities testing. A better method is to pump air through
the pet cock
Ref- Dr G.V Rao Phd
If any other result please send to my id -
mastalinprabu@gmail.com
With thanks
M.STALIN
| Is This Answer Correct ? | 2 Yes | 1 No |
What will be the effect if I use inverter as UPS mood?
HOw can we calculate power factor at HT side.
A copper wire of length l and diameter d has potential difference V applied at its two ends. The drift velocity is vd. If the diameter of wire is made d/3, then drift velocity becomes
types of arc quenching methodes
Is there any difference in AC current/ DC current carrying capacity of a conductor .What can be maximum current handling capacity of a 2.5mm stranded cu cable when connected to AC and DC supply.
If stator & rotor of a 3-phase induction motor have different no. of poles, will the motor run or not??
how we calculate the 30 KW 3phase electric motor current on noload
23 Answers Monnet, Siemens, SSR, Supermac Industries,
Sir, My doubt on cable sizing calculation, Load:74 KW calculated cable 1 run 50mm2. Now client asking us to reduce cable size by increasing runs. Sir, My question now when my mind strikes with 2 options 1) Divide load 74/2 = 36 and calculate cable for 36+36 making it 2 runs or 2) Simply i can divide 50mm2 /2 ie. 2 runs of 25mm2 Please suggest me sir
Ash AAAC conductor is used for which KV lines
What is power factor?How to improve power factor
what you mean ct ratio? why use 400/5a,200/5a,150/5a ?
Define unilateral circuit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)