What voltage is used in Directional earth fault relay? and
why?
Answers were Sorted based on User's Feedback
Answer / ekanadam patlavath
dc 110 voltage used for relay operating. for reverse power
operetion
| Is This Answer Correct ? | 7 Yes | 7 No |
Answer / rajesh bodduna
Open delta voltage is used to check the direction of fault,
i.e secondary voltages are connected in delta fashion with
open at one end . . The directional earth fault relay will
get volatge from open delta and currents from CT's as inputs.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / hamed
Directional Earth fault relay requires to Inputs line
Current and line voltage.
So in case of Current there are standard output of any CT
(either 1A or 5A).And for Voltage Inputs there is a
Standard Potential transformers witch give 110/(sqr.root of
3).
| Is This Answer Correct ? | 0 Yes | 4 No |
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
why should we place 9KV lightning arrestors in 11KV substation ?
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
the total iron closs in a transformer core at normal flux density was measured at 25hz and 5ohz and was found to be 250w and 800w respectively.the hysteresis loss at 50hz would be................?????
What should be the height of basement according to NBCC code?
Why the suply frequency in INDIA is 50HZ
how much insultion resistance 11kv cable.
what is the constructional difference between a power transformer and potentian transformer?
what is the transformer turn ratio formula and give some examples?
In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3
Please mention any books for electrical design load calculation for industrial,commercial(to select cable,breaker,bus bar,stator,)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)