800A 22KV TP OCB. explain
Answer / sudhakar g
OIL CIRCUIT Breakers are mainly used on the HT side like in Substations and the advantages of OCB is when ever arcing happens the Oil produces the hydrogen and it helps to reduce the Arcing, The disadvantage of the OCB mainly are there are not Eco friendly when the time of arcing, Oil in the Breaker decomposes and produce the carbon particles it pollute the air and if any defective OCB is installed means chances of Explosion chances are ther....In your case the 800A 22KV TP OCB means 22KV line used mainly in maharastra state 22/415V but in there also the Breaker used in HT panel also the rating is very low. Generally on HT side the HT panel breakers contain 2000A, 3200A like that but 800A is difficult to install on 22KV HT side....
Is This Answer Correct ? | 2 Yes | 0 No |
some ac motor's direction get change dueto ghanging input to the ac drives.(say ryb to rby). but some motor direction remains the same when phase sequence is changed fromdive side. can anybody guide me?
how to calculate maximum current
0 Answers Almeer Technical Services,
can we run all LT motors at 360 volts which are normally rated 415+/-10% voltage rating
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
when it is possible kvrah lead & fundamental kwh be equal in electonic trivector meters (3 ph)
There is 3phase power cable from 1 point to the other point which is 100m away. Two point equipped with power meter and recorded 1st point is 205kW while the 2nd is 202kW and each phase average carry 400amps. To calculate the resistance of the 3phase power cable, is the formula using will be P=I2R?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
The insulation resistance of a cable can be measured by
Why 30°phase shift occur in star-delta transformer between primary and secondary?
What is the difference between KV,KVAR,KVA,KW?
6 Answers L&T, PowerHouse, YUI,
Why we should not parallel the with EB
What is the function of a pressure Switch in a Substation?