what happens when power factor leads or lags to electical
or home appliances
Answers were Sorted based on User's Feedback
Answer / santhosh
due to use of lag p.f more reactive power consumed so
tariff can be increased
reactive power can be minimised by adding of lead p.f
means capacitors are connected at load ends
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / aftab ahmad
When PF leadd or lags there is requirement of more for same
power consumption.....
as
p=vi cos of angle between current and voltage
Is This Answer Correct ? | 3 Yes | 2 No |