IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP
TO 280
SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS
THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER
OUTPUT
EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Answer / sudhakar g
Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...
I=(93.75*1000)/(1.732*415v*0.8)
I=163A
this is the maximum current we can use at full Load then how you are using upto 280A....
I think it is not possible...Correct me if i am wrong...
In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
Define delay time.
What are the causes of eddy current losses?
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?
how to set earth fault relay
what is the current rating of 2500 KVA,33KV/433v transformer on secondary(LT) side
9 Answers Reddy Labs, Vitrum Glass,
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
what is phase to phase to phase to ground fault
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Direction of flow of active power and reactive power with logic?
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
hi plz send me reliance placement papers..i.e electrical technical papers that have been asked in reliance test.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)