IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP
TO 280
SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS
THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER
OUTPUT
EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Answer / sudhakar g
Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...
I=(93.75*1000)/(1.732*415v*0.8)
I=163A
this is the maximum current we can use at full Load then how you are using upto 280A....
I think it is not possible...Correct me if i am wrong...
In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 2 Yes | 0 No |
how to reduce earth resistance in sandy soil.
can we use ZNyn11 transformer instead of Dyn11 transformer in distribution for effectively eliminating harmonics from the industrial loads.
What is the difference between INVERTER and UPS?
in dc shunt generator field is open in running condition what will happen?
What is farmula to calculate Diesel cunsumption as par KVA.
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
how do i calc busbar size for a rated current?
If one 10 Hp 3phase induction motor connected in 380volt 50Hz. and again its connected to 380volt 60Hz. howmuch currrent and power take on both time?????
During the transients in alternator,the mechanical power input remains almost constant while the electrical power output changes significantly.Why?
Why star delta starter is preferred with induction motor?
why distribution transformer are of DY11 type?
How to justify this statement ??? "Capacitors in series provide less capacitance but higher voltage breakdown rating for the combination"