Answer / sudhakar g
Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...
I=(93.75*1000)/(1.732*415v*0.8)
I=163A
this is the maximum current we can use at full Load then how you are using upto 280A....
I think it is not possible...Correct me if i am wrong...
In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?
Why the power generated in dams is complex power? Why the generators in dams cannot produce Real power directly (i.e power which has zero reactive part)?
What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.
Can any body tell me the different types of LT cables & their application.
What are the essential parts of a transformer?
Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?
i have dry type transformers can you help me that how many tests i can do to know the performence of transformer and also please tell me about the BDV test and Insulation resistance test in oil cooled transformers
What is the Power factor of DC Power system ?
What happens to the synchronous generator when reverse power is given to it?
back emf of motor at the time of starting ?
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
How many gap between finger contact in a.c.b. and v.cb.?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)