what is the difference between UPS and INVERTER?
Answers were Sorted based on User's Feedback
Answer / vensa
ups means uninterrupted power supply which means it supplies
the power continuously when the supply fails without
interrupting the power
Inverter mean which converters the ac to dc supply to ac
supply.
| Is This Answer Correct ? | 9 Yes | 1 No |
Inverter will convert dc into ac supply.
But ups get a ac supply convert it into dc and store it in
a back up battery, and then dc is converted into ac supply
and then suppllied to cpu.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / p.k.ghosh
In UPS & inverter both are used for made D/C to A/C . In
inverter there is no PWM & we gets only quasi sine
wave .Where as in UPS there are PWM and we gets Sine wave.
For computer & other sofisticated devices required true
Sine wave hence UPS used & for lightning & other less
sofisticated equipments, inverter are used where required
only varing wave form which may not be true sine wave or
have quasi sine wave.
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / m.kumar
ups means any raw power supply is gone that time time used
for ups inverter is ac/dc function so used directly in
house .inverter capacity low and cost low.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.k.ghosh
In UPS & inverter both are used for made D/C to A/C . In
inverter there is no PWM & we gets only quasi sine
wave .Where as in UPS there are PWM and we gets Sine wave.
For computer & other sofisticated devices required true
Sine wave hence UPS used & for lightning & other less
sofisticated equipment required only varing wave form which
may not be true sine wave or have quasi sine wave used.
| Is This Answer Correct ? | 2 Yes | 11 No |
what is the difference between star connected and delta connected motors
how ship earthed?
why most of the induction motors are delta connected?
I need the recommended size for a 3 phase transformer at 13.8 KV Primary and connected loads of 3000 kVA at 4200 volts and 2375 kVA @ 480 volts AC.
How does CT can measure the high value DC current?
what is insulation percentage of motor 3 phase and singlephase
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
please design a rectifier with batteries for below requirement and also explain how you calculate this solution, Load = 700Amp DC Backup time = 6 hour. please explain briefly ?????
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
0 Answers Alam Group of Companies,
what is the merz prodution ? what is the turn to turn fault?
why only exciting current is shown not primary current in transformer???
Suppose the incoming power is 11 kw, but the load require only 8 kw means how can we save or use the excess power?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)