Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.


Answers were Sorted based on User's Feedback



How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shoyabkhan

the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP

Is This Answer Correct ?    24 Yes 6 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shashank

deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.

Is This Answer Correct ?    15 Yes 9 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / balakrishnan.t

For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor

OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps

Is This Answer Correct ?    6 Yes 3 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shamsher singh

10sqmm cooper

Is This Answer Correct ?    1 Yes 1 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / ramesh insan

As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85

1.732*415*0.8*0.85=488.77

30HP*746W=22380/488.77=45.79 Amp

Is This Answer Correct ?    0 Yes 0 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / amarnath

If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.

And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.

Is This Answer Correct ?    17 Yes 23 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / mrudang

we are measure through SWG ( standard wire guage
it measure the crossection of wire
2.5sqmm

Is This Answer Correct ?    13 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

why we are using KVA rating for transformer,not KWh rating?

5 Answers   NTS,


What is the difference between Generator Differential Relay and Transformer Differential Relay?

0 Answers  


In the diesel generator if there is an AVR (auto voltage regulator) gone faulty, in this condition is there any way to generate the voltage from the alternator? I need a brief explanation can you please help somebody

1 Answers   Vodafone,


What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?

2 Answers   DLF,


what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing

0 Answers  


What is the distance b/w R&Y phase in 33kv T.line,11kv &440v

1 Answers   NTPC,


What is the difference between a verilog task and a verilog function?

0 Answers  


Application wise, where we should use AC motors and where we should DC motors?

1 Answers   Nespak,


why we use the 100% and 95% stator earth fault protection for the synchronus generator ?

0 Answers   Operational Energy Group,


- two pumps must work with them at the same time but if the first pump start the second pump  must delayed for some time to start  also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it

0 Answers  


why co incidence factor considered in transformer sizing?

0 Answers  


why we use star connection in HT motor? and delta connection in LT motor

2 Answers   npcc,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)