How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.
Answers were Sorted based on User's Feedback
the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / shashank
deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / balakrishnan.t
For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor
OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ramesh insan
As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85
1.732*415*0.8*0.85=488.77
30HP*746W=22380/488.77=45.79 Amp
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amarnath
If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.
And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.
| Is This Answer Correct ? | 17 Yes | 23 No |
What is floating voltage?
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
Why indicate only 440V to 3-phase supply.
How Calculet The UPS AH In Load
what will happen if frequency is below 50 hz?
what is softstarter?
how unidirectional torque is produced in DC motor?
types of central Air conditioner plant?
power requirement of an l.e.d?
definition of transformer
how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)