Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.


Answers were Sorted based on User's Feedback



How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shoyabkhan

the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP

Is This Answer Correct ?    24 Yes 6 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shashank

deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.

Is This Answer Correct ?    15 Yes 9 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / balakrishnan.t

For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor

OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps

Is This Answer Correct ?    6 Yes 3 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / shamsher singh

10sqmm cooper

Is This Answer Correct ?    1 Yes 1 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / ramesh insan

As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85

1.732*415*0.8*0.85=488.77

30HP*746W=22380/488.77=45.79 Amp

Is This Answer Correct ?    0 Yes 0 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / amarnath

If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.

And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.

Is This Answer Correct ?    17 Yes 23 No

How you calculating the current for a 2.5 Sqmm cable. A 30 Hp 3 phase AC motor of power what size o..

Answer / mrudang

we are measure through SWG ( standard wire guage
it measure the crossection of wire
2.5sqmm

Is This Answer Correct ?    13 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

1 KW = how many kva

4 Answers  


Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?

0 Answers  


what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct

0 Answers  


What is the function of Harmonics filter, and how to calculate that rating of the energy saving?

1 Answers  


How can we select a capacitor Bank.? i need a standard formula for that.?

3 Answers   ABB, Ace Info, HAL, IKK, MahaGenco,


what is the physical connection of a analog i/p to a analog i/p module (ab plc)and through a analog o/p module(ab plc) to a analog o/p . and how all the process control by scada

0 Answers  


in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses?  the second question is-generation is depends on LV winding? or LV winding design for generation voltage?

0 Answers  


Spacing of Transformers ratings are 10kva,15kva,25kva,63kva,110kva,150kva .........so on Q) Why transformer are not manufactured having ratings in between or other than these standard ratings ?

3 Answers  


why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently

4 Answers  


What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?

0 Answers   Bhad Engineers,


Why the rotor winding is short circuited of induction motor

1 Answers  


i want to ask that as everybody knows that in star connection on star point is called neutral. my question is that why on that poin called neutral. what is the reason behind it. what is the logic behind it. i heared somewhere that on this point all phases current become zero thats why. if this answer is right then prove why on that point is current become zero. if this answer is not right then tell me the right answer. post ur answer here or on my mail address. m.ikram786@yahoo.com m.ikram555@gmail.com. thanks.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)