How you calculating the current for a 2.5 Sqmm cable.
A 30 Hp 3 phase AC motor of power what size of cable is
used for this motor.
Answers were Sorted based on User's Feedback
the answer is wrong we can calculate by usbing this formula
W = 1.732*V * I Cos (phi)
30*746 = 415 * I * 0.8*1.732
I=36.2 AMP
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / shashank
deciding a cable has to consider following parameters also,
1. Safety factor of the cable (margin for starting current
say 1.25 in numerator side)
2. Deterioration / Degradation factor (say 0.8 in
denominator)
calculate the current of the motor by considering running
pf (power factor) say 0.8
as motor gives real power
e.g.
W = V * I Cos (phi)
30*746 = 415 * I * 0.8
I = 30 * 746 / (415*0.8)
I = 67.41 Amp,
Thus Current considered for cable (Icb) = 67.41*1.25/0.8
Icb = 105.3 Amps.
Select from the catalogue suitable copper cable for this
motor. Dont forget to consider the voltage drop per meter,
the total voltage drop shall not be more that + - 5%.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / balakrishnan.t
For calculating the current rating of a 30 Hp 3 phase motor can be written as
power = sq root(3)* VL*IL*cos (phi)--------(1)
where 'VL' is line voltage, 'IL' - line current and cos phi- power factor
OR 3 EP*IP*cos(phi)
as the voltage fed is from three phase system.
Power input of 30 Hp motor = 30*746/(efiiciency*cos phi) watts
from the formula (1) and taking efficiency as 0.9,
Line current 'IL' = 30*746/(1.732*415*0.9*0.83)
= 41.68 Amps
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ramesh insan
As per thumb rule
Power Sq root 3=1.732
Voltage =415
PF=0.8
Cos=0.85
1.732*415*0.8*0.85=488.77
30HP*746W=22380/488.77=45.79 Amp
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amarnath
If its a 2.5Sq.mm Aluminium cable then it can take load
current upto 3Amps and if its Copper cable then it can take
a load current upto 9.4Amps.
And for a 30HP motor the cable size shall be 3.5Core X
16sq.mm Aluminium or 3.5Core X 6sq.mm Copper cable.
| Is This Answer Correct ? | 17 Yes | 23 No |
when power transformer is flashed which gas is produce in side?
what is the main parts of DG? how it is working?
how work the lighting arrestor?
sir pls send the je exam - 2008 and other model question papers..
what is the main function of contactor?????
Can u Explain about the electronic trivector meter and the use of data converters in them?
what will happen when two dc motors are connected to each other and anyone of them rotated?
how braking & making capacity of circuit breaker is calculated?
how maney type tempereture measurement ?
how cables go in and come out for distribution from the feeder pillar box?
what will happen if i commission a transformer without connecting the neutral?
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)