Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?

Answers were Sorted based on User's Feedback



Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?..

Answer / b_saravanakumar

We can use 0-10 volt also for signal. But while signal
transmission voltage drop will occur on lead wires. Also
voltage will have noise due to this we may loose signals at
receiving end. To overcome this we are using current
(4-20mA) for signals.

Is This Answer Correct ?    16 Yes 7 No

Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?..

Answer / priyabrata samanta

The reason is - if we use 0 to 10 volt range then even if
an error occur in the transmission line we will not be able
to identify it. As there will not be any way to compare this
state with zero signal.
Whereas in 4to 20 ma current range we will be able to
compare the fault in the transmission line with zero
signal(4 ma).
Another reason is that using voltage as a transmission
signal is unfaithful and erroneous. As there will be voltage
drop in the transmission line , and therefore true signal
will not be received at the receiving side. But if we use
current as the transmission signal then noise can effect the
transmission, but "current drop" will never happen.

Is This Answer Correct ?    9 Yes 0 No

Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?..

Answer / dev

Answer related to 0-10V is voltage drop as all frnds said
above but why 4-20mA preferred is as below:

Actually, you can use any range you want! But if you do, you
will have to design and manufacture both the transmitter and
receiving controller to match.
The 4-20 ma range is a "standard" adopted by tradition and
also ANSI 50.1, and most process instruments and controllers
use it. It was developed during a time when teletypewriters
used a 20 ma current loop for communications, so parts for
that type of circuit were readily available. There once was
a 10-50 ma current loop, but it has pretty much faded out.
It does have several advantages:

* The 4 ma "bottom of span" signal allows the receiver
to detect a broken wire or failed instrument.
* Since the loop current never falls to zero, the
instrument can be loop powered, allowing for two-wire devices.
* 20 ma is low enough to be made intrinsically safe,
making it easier to apply in hazardous locations.
* The constant-current feature of a current loop cancels
out voltage drop errors due to long wiring runs (of course
this would also be true if you selected different current
values for zero and span).
* The 4-20 ma signal dropped across a 250 or 500 ohm
resistor creates a very convenient 1-5V and 2-10V,
respectively, also fairly standard ranges in the industry.


So, while technically a manufacturer could use 7-17.3 ma or
6.2-21.1V as their range, who would buy their pressure
transmitter? No one! That's both the beauty and trap of a
"standard". There is a huge investment out there in process
controls that use 4-20 ma. That's the real reason, Im
afraid. You will not change that until you find a different
range that has some huge benefit over the current (pun
intended) standard.

In short bottom span is 4mA which is standard bcoz if any
instrument is dead and have 0 o/p then we won't detect what
actually is because both gives 0 o/p....... and
standardization of 4-20mA is as above....

Hope Got It....

Reference:copy and paste this link u will get what i
got>...::::


http://wiki.answers.com/Q/Why_does_the_process_industry_use_a_4-20ma_range_for_signal_processing_why_cant_you_use_different_ranges

Is This Answer Correct ?    9 Yes 0 No

Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?..

Answer / eid elatawy

L
The resistance R= Resistance const * ---
A

Where L the length of the conductor
and A section area of the conductor

form the above equation we can note that the resistance change
the length of cable so the length of cable affect on signal (V) according to Ohm's Law
V=I*R
so, in case of long distance will affect on the accuracy of the signal.


Regards
Eid Elatawy
I&C Engineer
TCI Sanmar chemicals CO
Contact no 002 01000470262

Is This Answer Correct ?    0 Yes 0 No

Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?..

Answer / vijay kumar

Generally in a transistor some amount of voltage is
required for turning it on. This voltage is the cut in
voltage. Up to this voltage the exists a nonlinearity in
its characteristics. Beyond this cut in voltage the char.
of transistor is linear. This nonlinear region lays between
0-4ma, beyond 4ma it linear. This is why 4-20 ma range is
used.

Is This Answer Correct ?    4 Yes 18 No

Post New Answer

More Instrumentation Interview Questions

[ MITUTOYO / TESA / KUMAUN / MAHR / BRITOOL / TOHNICHY / DIATEST-GERMANY / IMADA / TECKLOK / SYLVAC /ADITYA=ACCURATE / BAKER/ CRYSTAL / FLUKE-RAYTEK ETC. 5.=SUPPLY= VERNIER CALIPERS / MICROMETERS / HEIGHTGAUGES / SLIPGAGE / BORE DIAL GAUGES / MEASURING PINS / TORQUE WRENCHES / GAUGES.. PLUGGAUGES / RINGGAUGES / SHORE A / D HARDNESS TESTERS / DIAL THICKNESS GAUGE / FEELER GAUGES / ELECTRONIC COMPARATORS WITH PROBES / DFTMETERS / SURFACE ROUGHNESS TESTERS / DIGITAL= COATING THICKNESS METERS / PROFILE PROJECTORS /.. WE ARE ALSO DEAL IN == DIGITAL TACHOMETERS / =MULTIMETERS! / VIBRATION METERS / MEGERS- INSULATION METERS / =TE! MPRATURE INDICATORS / SOUND-LEVEL METERS / ETC... =AGENCY- FLUKE- RAYTEK.. MECO....LUTRON...KYORITSU....RION

0 Answers  


HOW TO SOLVE PROBLEM WITH ENRAF LEVEL TRANSMITTER 854 ATG THAT PASSWARD DO NOT Exist INTO TRANSMITTER TO ADJUST LEVEL WITH PORTABLE PET 847, WRITTEN WRONG PASSWORD , I AM SURE THAT DEFAULT PASSWARD (W2=ENRAF2) IS THIS TRANSMITTER NEED TO REPLACE SOFTWARE AND HOW?

0 Answers   Lerco,


Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: &#916; P allow = Km (P1 – PvapourA) where, &#916; P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72

0 Answers  


I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.

0 Answers  


Q- Ordinary Water Tap is which kind of controller ? P , PI or PID i chose the option of ON - OFF type controller but ambiguity is that for different positioning of tap we get different flow

1 Answers  


What is rang ability?

0 Answers  


how to measure low temperature(<100 dec celsisus) with non condact sensor

2 Answers  


What is the difference between HMI and MMI?

16 Answers  


What are the different modes of a contollogix family processor? How they work?

3 Answers   Honeywell, Siemens,


Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?

2 Answers  


I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea

3 Answers  


in mass flow meter what is drive friquancy ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)