how can we measure the pressure in underground cooling
water pipeline by using pressure transmitter?what about the
tapping position?
Answers were Sorted based on User's Feedback
You can install the PT anywhere on the pipe. It is best to
install on top in crude and slurry application but to
measure water you can install any where, even under the pipe.
If you install on the side or under the pipe fill the
impulse line with water then do a zero on the PT before you
do the final span calibration. Also remember that the
calibration you do on the PT must be exactly the same as to
what your DCS or SCADA faceplate have been scaled to. In
other words if you calibrate the PT for 0 to 20Bar you must
make sure the faceplate in the CCR are also scaled to 0 to
20bar.
Good luck
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
If the transmitter is not directly mounted on the
underground pipe, which is not unusual unless there is
vault access, then an impulse tube/pipe has to come up out
of the ground. The pressure measurement will be in error,
low, by the difference in elevation between the pipe's
elevation and the pressure transmitter's elevation.
Suppose the pipe is 2.1m below the grade level and the
pressure transmitter is 1.6m above grade. The elevation
difference is 3.7m.
The measurement is 3.7m or 0.362 bar low.
It is not unusual to have water supplied at pressure
between at 4-8 bar. At 4 bar pressure, an error of 0.36m
water column is a 9% error, a vary large value for an
insturment capable of 0.25% or better accuracy.
The commissioning of the unit should include the
appropriate zero correction to compensate for such a large
error.
Carl Ellis, Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
I WANT TO KNOW SOME BASIC CONCEPTS RELATED TO INSTRUMENTATION
we have LPG spherical Tank and we want to install DP Xmtr for level measurement.below are the physical measurements Total height of tank is 1850 mtr but 0% level is 1000mm above bottom and 100% level is 450 below upper side.What is the LRV and URV and please mention the formula .The SG of LPG is 0.53 and Wet Leg method will be used.
Describe the function of Accumulator into the Pump
In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?
1 Answers Process Control Technologies,
what is protonics how it is differ from electronics
What is input and output of plc & dcs
i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
Explain plc level and its type?
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
2 Answers Gujarat Fluorochemicals Limited (GFL), Shell,
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
[ MITUTOYO / TESA / KUMAUN / MAHR / BRITOOL / TOHNICHY / DIATEST-GERMANY / IMADA / TECKLOK / SYLVAC /ADITYA=ACCURATE / BAKER/ CRYSTAL / FLUKE-RAYTEK ETC. 5.=SUPPLY= VERNIER CALIPERS / MICROMETERS / HEIGHTGAUGES / SLIPGAGE / BORE DIAL GAUGES / MEASURING PINS / TORQUE WRENCHES / GAUGES.. PLUGGAUGES / RINGGAUGES / SHORE A / D HARDNESS TESTERS / DIAL THICKNESS GAUGE / FEELER GAUGES / ELECTRONIC COMPARATORS WITH PROBES / DFTMETERS / SURFACE ROUGHNESS TESTERS / DIGITAL= COATING THICKNESS METERS / PROFILE PROJECTORS /.. WE ARE ALSO DEAL IN == DIGITAL TACHOMETERS / =MULTIMETERS! / VIBRATION METERS / MEGERS- INSULATION METERS / =TE! MPRATURE INDICATORS / SOUND-LEVEL METERS / ETC... =AGENCY- FLUKE- RAYTEK.. MECO....LUTRON...KYORITSU....RION
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)