Answer / c.tharakeswara reddy
In open circuit test HV is open, LV is connected to supply
meters also connect to lv side why because availabilty of
high range voltmeters is not easy(hv voltmeters are
costly),conductnig test on lv or hv we get same result.so
why need to conduct on lv side and make experiment costlier.
In short circuit test LV is short circiuted HV is connected
to supply,meters also connected to hv side. sc test is
conducted on rated current.HV side current is low so we can
use low range ammeters.conductig test on lv or hv we get
same result.if we condct test on hv we need high rage
ammeters. it makes experiment costlier.
| Is This Answer Correct ? | 156 Yes | 66 No |
Answer / nitish prajapati
short ckt test is performed at rated current,as the rated current on hv side is much less than lv side so the rated current is easily achieved(compared to lv side).
| Is This Answer Correct ? | 59 Yes | 6 No |
Answer / imtiyaz rasool
short circuit test is conducted on LV side because the voltage on LV side is low compared to HV side so their is less chance of getting shock from low voltage on LV side
| Is This Answer Correct ? | 5 Yes | 40 No |
why transformer is rated in kva instead of kw?
you are a electrical student, why are you coming for software job.
In a voltage-controlled current source A A current booster is never used B The load is always floated C A stiff current source drives the load D The load current equals Isc
What is the ideal power factor?
How to find HT side and LT side(of a transformer),with the help of a voltmeter?
1 Answers Odisha Power Generation Corporation OPGC,
what is corona ?
why ac supply neutral should earth not in dc (-)
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
why are using bus ducts ? why not using cables
why the electrical insulators suspention breakdowen
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)