Why we use 4 to 20 mA, (This is International Standard)
instaed of this can we use 4-16, or 4-24 or 3- 15 or any
other range
Answers were Sorted based on User's Feedback
Answer / nagarajan.p
First the question is why can't we use 3~15mA or other
range, here also we can check live zero and also we can go
step current like 3,6,9,12,15(i.e 0%,25%,50%,75%,100%).ok
The reason is the transmitter voltage is 24Vdc , here we
can load max of 600 ohms, for this voltage & load better
range is 4~20.
Why 4 ~ 20 is better since we can convert easily 1~5Vdc by
put 250 ohms.All the controllers and DCS , PLCs are operated
by the input of 1~5Vdc (external or Internal convertion)
| Is This Answer Correct ? | 47 Yes | 5 No |
Answer / nilesh upadhyay
There are basically 2 reasons of using 4-20ma
1. we can know whether the instrument is working properly
or not. we can distinguish "live zero" and "dead band". if
there is problem in instrument then also it is going to
show zero and if there is no supply then also it will show
zero so we can differentiate this two.
2. 4-20ma is linear with 3-15psi .
Nilesh Upadhyay...
| Is This Answer Correct ? | 23 Yes | 12 No |
Answer / richard marks
the 4mA zero is termed a "live zero". If 0mA was the zero
point there would be no way of telling if the transducer
was reading zero or in a fault condition eg. an open loop.
with a 4mA zero an open loop would drive the indicator eg.
a recorder into a minus figure (-25%). The 4 - 20mA scale
is to give a calibration points for 0-25-50-75-100%.
Because the start point is 4 the steps are 4mA.
| Is This Answer Correct ? | 14 Yes | 6 No |
Answers 5 & 6 are totally correct.. just adding another point.
20 mA as upper value is used to keep electrical components
intrinsically safe at hazardous area.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / dhaval joshi
for any active ckt make it standard 1 volt dc
actually formula is 20-4= 16 then
16/1000*250=4 ma
32/1000*250=8 ma
48/1000*250=12 ma
64/1000*250=16 ma
80/1000*250=20 ma
by using 250 ohm resistance and standard 1000 ma it give
standard voltage.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / rajesh.a
STANDARD VOLTAGE IS 1-5V DC,250OHM RESISTANCE
AT V=I*R
AT 1V=I*250OHM = 4MA
AT 5V=I*250 OHM = 20MA
SIMPLE CALCULATION
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anup ramteke
Answers 5, 6 & 7 are correct. just want 2 add that why cant
we use 3 mA current as lower value. The reason is that there
are many small noise signals that can be picked up by our
signal wire which has the potential of providing upto 3 mA
current. So to be on the safe side to distinguish between
our proper field signal and the noise pick-ups we use 4 mA
as our lower value
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / abdus sattar mollah
ALL ANSWERS ARE WRONG.....
4-20 is a standard because transistor which is the basic building block of any transmitter has a linear output charecteristics in 4-20ma range.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / mayur
ans. 5,6,7 & 8 r correct.only two points add.
1.in ancient time,niddle type galvanometers are used,only if
we pass 4mA current it shows deflection.therefore 4mA.
2.if 21mA current will pass through our body,man can goes
dead.therefore 20mA. & 4-20 mA can divided into 5 equal %.
| Is This Answer Correct ? | 4 Yes | 12 No |
Do you have reference list?
WHICH IS BEST INSTRUMENTATION OR ELECTRICAL ENGG?
Different between control valve and mov
what is the working principle of hydra step(electronic level indicator)?
2 Answers Bengal Energy, Lanco,
In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
what is the difference between AUTOMATION AND INSTRUMENTATION?
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
what is formula for calculating flow if i have pressure and pipe diameter?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
Explain PID controller tuning & any one method used for it.
difference between vaccum and draft
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)