Answer / nagarajan.p
First the question is why can't we use 3~15mA or other
range, here also we can check live zero and also we can go
step current like 3,6,9,12,15(i.e 0%,25%,50%,75%,100%).ok
The reason is the transmitter voltage is 24Vdc , here we
can load max of 600 ohms, for this voltage & load better
range is 4~20.
Why 4 ~ 20 is better since we can convert easily 1~5Vdc by
put 250 ohms.All the controllers and DCS , PLCs are operated
by the input of 1~5Vdc (external or Internal convertion)
| Is This Answer Correct ? | 47 Yes | 5 No |
Answer / nilesh upadhyay
There are basically 2 reasons of using 4-20ma
1. we can know whether the instrument is working properly
or not. we can distinguish "live zero" and "dead band". if
there is problem in instrument then also it is going to
show zero and if there is no supply then also it will show
zero so we can differentiate this two.
2. 4-20ma is linear with 3-15psi .
Nilesh Upadhyay...
| Is This Answer Correct ? | 23 Yes | 12 No |
Answer / richard marks
the 4mA zero is termed a "live zero". If 0mA was the zero
point there would be no way of telling if the transducer
was reading zero or in a fault condition eg. an open loop.
with a 4mA zero an open loop would drive the indicator eg.
a recorder into a minus figure (-25%). The 4 - 20mA scale
is to give a calibration points for 0-25-50-75-100%.
Because the start point is 4 the steps are 4mA.
| Is This Answer Correct ? | 14 Yes | 6 No |
Answers 5 & 6 are totally correct.. just adding another point.
20 mA as upper value is used to keep electrical components
intrinsically safe at hazardous area.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / dhaval joshi
for any active ckt make it standard 1 volt dc
actually formula is 20-4= 16 then
16/1000*250=4 ma
32/1000*250=8 ma
48/1000*250=12 ma
64/1000*250=16 ma
80/1000*250=20 ma
by using 250 ohm resistance and standard 1000 ma it give
standard voltage.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / rajesh.a
STANDARD VOLTAGE IS 1-5V DC,250OHM RESISTANCE
AT V=I*R
AT 1V=I*250OHM = 4MA
AT 5V=I*250 OHM = 20MA
SIMPLE CALCULATION
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anup ramteke
Answers 5, 6 & 7 are correct. just want 2 add that why cant
we use 3 mA current as lower value. The reason is that there
are many small noise signals that can be picked up by our
signal wire which has the potential of providing upto 3 mA
current. So to be on the safe side to distinguish between
our proper field signal and the noise pick-ups we use 4 mA
as our lower value
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / abdus sattar mollah
ALL ANSWERS ARE WRONG.....
4-20 is a standard because transistor which is the basic building block of any transmitter has a linear output charecteristics in 4-20ma range.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / mayur
ans. 5,6,7 & 8 r correct.only two points add.
1.in ancient time,niddle type galvanometers are used,only if
we pass 4mA current it shows deflection.therefore 4mA.
2.if 21mA current will pass through our body,man can goes
dead.therefore 20mA. & 4-20 mA can divided into 5 equal %.
| Is This Answer Correct ? | 4 Yes | 12 No |
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
What is furnace draft control?
While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.
model question paper of instrumentation for Jindal GET 2010.plz reply sudhanshukumar08@yahoo.com
please explain clearly in PID controller if We increase P only what will be action of the contrlere.
Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000
what is the calibration procedure for transweigh make weigh feeder?
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
How comparison of objects is done in PHP5?
why use to 250 ohm for hart protocol and why hart communicator not communicate without 250 ohm
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)