Do you know how to measure the earth resistance? if so explain it..

Answer / bipin kumar mishra

earth resistance can measure by earth testor/earth resistor.

Is This Answer Correct ?    16 Yes 7 No

Do you know how to measure the earth resistance? if so explain it..

Answer / ravindra

earth resistance is measured by earth tester

Is This Answer Correct ?    12 Yes 5 No

Do you know how to measure the earth resistance? if so explain it..

Answer / naveen kumar mishra(03\08\1987

the most easy to calculate the specified earth
resistance,is by using earth testor.
a earth testore is a electric generator which generate the
electric voltage as per constant speed of that rotor
(generator).
if any low resistance load will apply across that voltage
so an electric current will also generate.
by this current,and voltage,we can calculate the value of
applied load resistance.
so lets assume----------
the voltage value generated by earth testor

is = V volts,

and current value is = I amp

so according ohms law

the applied load value will(earth resistance) = R

SO R =V/R ohms.

Is This Answer Correct ?    17 Yes 10 No

Do you know how to measure the earth resistance? if so explain it..

Answer / ssreenu

Mr. Dinesh, please tell me at what distance(min & max) the
spikes to be placed from earth electride and how much
distance(min and max) should be kept between the earth
spikes?

Is This Answer Correct ?    9 Yes 6 No

Do you know how to measure the earth resistance? if so explain it..

Answer / rajkishore parida

Visit the website
http://www.kilowattclassroom.com/Archive/AN0009.pdf - 91k -
This is the best site where one can get the best answer on
how to measure the earth resistance and all the related
information.

Is This Answer Correct ?    10 Yes 8 No

Do you know how to measure the earth resistance? if so explain it..

Answer / yogesh

the current being supplied from the AC power lines.
Alternatively, a bridge may be
used for measurement. Most often, the ground resistance is
measured with selfcontained
instruments such as the Megger ground resistance Tester.
The resistivity of earth may vary over extremely wide
limits, depending on the
composition of the soil and the moisture content.
Representative values are:
General average 100 ohm-meters
Swampy ground 10-100 ohm-meters
Sea water 0.01-1 ohm-meters
Dry earth 1000 ohm-meters
Pure slate 107 ohm-meters
Sandstone 108ohm-meters
Fig. 2 Equivalent radius A of groups of ground rods of
radius "a"
I current
V voltmeter
Ground under test Reference ground Auxiliary ground
Fig. 3 Fundamental method of ground resistance measurement
TYPE 3235 Earth TESTER
Adequate earthing systems for telecommunications,
electronic and electrical
equipment, power lines and lightning arresters of steel
towers and high buildings are
of extreme importance. Good earthing systems safeguard
personnel and equipment
during fault conditions. They are also frequently necessary
in minimising electrical
noise and for normal, reliable operation of electrical and
electronic equipment. The
resistance of any earthing system should be periodically
checked to ensure that it is
within limits.
The Type 3235 Earth Tester can be used to check almost any
earthing system. It
incorporates a test for earth voltage. AC voltage up to 30V
may be measured. High
S S S
S S S S
A=SQRT(a S ) S
A= cube root of(aS2) A= fourth root of(sqrt(2)aS2)
S

Is This Answer Correct ?    15 Yes 13 No

Do you know how to measure the earth resistance? if so explain it..

Answer / s. ghosh

earth resistivity is measured by earh megger . there so
many methods of earth resistivity measurements like1)
wenner 4 pin method, 2) schlumberger method, 3) driven rod
or 3pin method. all those test results varies on different
parameters of the site. to minimise tose effects the tests
has to be performed in an arrey called"line traverse
servay". the detail of those above methos i.e. the distace
of rod depth of rod and their variation is to be discussed
in detail. however the result given by the "earth megger"
i.e. the resistance of earth is to be converted into earth
resistivity by the following formula.
Wenner method:-
r(resistivity) = 2(PI)A R : A =Probe spacing, R
resistance reading in the E/megger
Schlumberger:-
r=(PI) L.L.R/2.l L=centre limb to outer probe,
l=centre limb to inner probe,
Driven rod:-
r=2(PI)lR/Ln(8l/d) l=rod length in earth, d=dia of rod.
contact me at sgmanofpower@yahoo.com if you have got
further details or questions.

Is This Answer Correct ?    12 Yes 10 No

Do you know how to measure the earth resistance? if so explain it..

Answer / zeenath

s i do...it should be less than 1 ohm..for any
clarification plz call me at 09036571568..

Name: Zeenath Kundur
Mobile: 09036571568
Official ID : zeenath.kundur@prithvisolutions.com

Thanks and Regards,

Zeenath Kundur
Project Manager
Prithviinformation Solutions LTD

Is This Answer Correct ?    7 Yes 5 No

Do you know how to measure the earth resistance? if so explain it..

Answer / nurul islam mallick

The Fluke 1625 earth ground tester is able to measure earth ground loop resistances for multi grounded systems using only current clamps. With this test method, two clamps are placed around the earth ground rod or the connecting cable and each are connected to the tester. A known voltage is induced by one clamp, and the current is measured using the second clamp. The tester automatically determines the ground loop resistance at this ground rod.



Ideally a ground should be of zero ohms resistance.
There is not one standard ground resistance threshold that is recognized by all agencies.

However, the NFPA and IEEE have recommended a ground resistance value of 5.0 ohms or less.

The NEC has stated to “Make sure that system impedance to ground is less than 25 ohms specified in NEC 250.56. In facilities with sensitive equipment it should be 5.0 ohms or less.”

The Telecommunications industry has often used 5.0 ohms or less as their value for grounding and bonding.

The goal in ground resistance is to achieve the lowest ground resistance value possible that makes sense economically and physically.

Is This Answer Correct ?    2 Yes 0 No

Do you know how to measure the earth resistance? if so explain it..

Answer / tofan kumar sahu

Earth resistance should be mesured only by using earth
tester the potential spike must be placed minimum 10mtr
away from mesuring earth pit & auxulary spike must be
placed minimum 10mtr from potential spike.That means the
distance between 2 spikes +the distance between earth pit &
potential spike should not less than 20mtr.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?

4 Answers  


234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,

0 Answers   Jubail O&M,


Is electro plating what type of load whether resistive, inductive or capacitive loads

0 Answers   Apollo,


What is VCB? where it is installed at SP. What is SP?

0 Answers  


Which types of Gases occure when mineral oil burnt

1 Answers  






why neutral busbar size is half of the phase busbar size in control panels

1 Answers   IBS,


Re: how to calculate diesel consumption of a D.G.Set? Answer # 1 We can not calculate the diesel comsumption...depending upon load it will conume the diesel...suppose the 1500kva D.G is running and the load is 1000kw means it will consume 150-200 liters per hour....

6 Answers   Cipla,


what is spill current?

4 Answers   Adani, NPCIL,


Give some differences between open loop and closed loop control systems.

0 Answers   GE,


can i know how to design overcurrent setting and earth fault for 11kv & o.433kv system assuming tx 1000kva.

2 Answers  


what is meant by flywheel and its role in retardation test

0 Answers  


what is the difference between dry and wet type of 132kV terminations. which one is durable

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)