Do you know how to measure the earth resistance? if so
explain it
Answers were Sorted based on User's Feedback
Answer / syed ahmed
i dont know so thats why iam asking how to measure the
earth resistance.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / segun
yes this is done using resistivity meter(terrameter) with
fou electrode,
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / mahesh m
Earth resistance is measured by using earth Resistance
meter. it is using for four probe method.Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.for current.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / balaji
earth resistance is measured my earth megger instrument. it
has three terminals
1) earth
2) line
3) ground
in this ground is for meter protection and earth is meant for
point of starting of measurement , line is meant for point
until which the earth resistance to be measured
this works on principle that emf generated by the generator
is forms a close loop when the points between earth and line
conducts that is meter will indicate zero incase of the
failure of earth resistance
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / sandeep
@R.sarkar
can you tell me at what distance and angle the two reference
electrodes P2 and P3 can be placed.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ankush shedge
Earth resistance is calculeted or measure by only Earth
Resistance Meter and that meter is prepared for specialy
earth resistance checking.Earth resistance must be less
than 1 Ohm if resistance increses Earth-Nutral voltage is
increses so maintain the earth nutral voltage resistance is
required less than one Ohm.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / amit lukka
The answer written by By Mr.R. Sarkar & Mr. Dinesh R. are similar and correct, one thing is to be added that P2 and P3 are reference electrode and are placed 50 Ft. away from the pit and another reference will be 100 ft. from the pit and deep 1 meter.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / dr. joshy jose
Earth resistance is mwasured by using earth resistivity
meter. It is by using four probe method. Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.
| Is This Answer Correct ? | 19 Yes | 21 No |
Answer / rajshekhar jangnure
there are four terminals p1,c1,p2,c2 outof this earthing
electrode connected to p2 and p1 &p2 get shorted There are
three electrods which are 60 to 70 feet equal distant from
eachother along withearthing electrode whose earthresistant
tobecalculate .then set 10 oham range & connect all
electrodes as mentions above by 1.0sq mm wire & rotate the
handle with constant speed & note the
reading
| Is This Answer Correct ? | 10 Yes | 18 No |
Answer / prashant
earth resistance measure can using megger instruments
| Is This Answer Correct ? | 75 Yes | 89 No |
Metal covered multiconductor cables shall employ a marker tape located within the cable running for its complete length in lieu of cable surface marking. Is it true or false?
whats is MARX CIRCUIT?
what is meant by Ac & DC drives where its useful ? how its functioning ?
WHat is the general checks required for Dry type transformers
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
what should be distance between two electrical earthing pit as per i.e.e
why we don't discuss power facter in dc?
what are all the daily preventive maintainance carried out in transformer?
WHAT IS THE HIGHEST UNDERGROUND TRANSMISSION VOLTAGE IN THE WORLD?
what is EIB lighting control system? what is the advantages of this system?
I've heard that most of the substations are rated in multiples of 1.11 because of form factor.What is form factor?
how is motorized megger operate?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)