Do you know how to measure the earth resistance? if so
explain it
Answer Posted / s. ghosh
earth resistivity is measured by earh megger . there so
many methods of earth resistivity measurements like1)
wenner 4 pin method, 2) schlumberger method, 3) driven rod
or 3pin method. all those test results varies on different
parameters of the site. to minimise tose effects the tests
has to be performed in an arrey called"line traverse
servay". the detail of those above methos i.e. the distace
of rod depth of rod and their variation is to be discussed
in detail. however the result given by the "earth megger"
i.e. the resistance of earth is to be converted into earth
resistivity by the following formula.
Wenner method:-
r(resistivity) = 2(PI)A R : A =Probe spacing, R
resistance reading in the E/megger
Schlumberger:-
r=(PI) L.L.R/2.l L=centre limb to outer probe,
l=centre limb to inner probe,
Driven rod:-
r=2(PI)lR/Ln(8l/d) l=rod length in earth, d=dia of rod.
contact me at sgmanofpower@yahoo.com if you have got
further details or questions.
Is This Answer Correct ? | 12 Yes | 10 No |
Post New Answer View All Answers
What are the weight of 800KV DA,DB and DC type tower ?
How will polarity test of Dy5 Transformer ?
why does rotor rotets?
Batteries used for electrical energy storage are a. Laclanche cells b. Edison cells c. Lead acid cells d.any of the above
Whether should be the oil level in OCTC transfomer? It should be upto winding immersed completely or should be upto tap changer s/w? How it will affect the performance of the transformer. Rating may be 33KVA
How to calculate Air conditioning capacity for a telecom BTS shelter?
what is earth resistance? how to measured? and give values at power station and mcc area?
How will change the frequency in distribution side?
Which motor connection is preferable star-delta or delta-star?
what clearance required for 4.5 mva dry type transformer?
can u give me a brief idea about power line carrier communication ??
what are the possible reaons & remedies if resistance of NGR getting heat up
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side
Name two types of electrical analogous for mechanical system.
What is the classification of hydro projects based on installed capacity?