Do you know how to measure the earth resistance? if so
explain it
Answers were Sorted based on User's Feedback
Answer / dinesh. r
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
Is This Answer Correct ? | 477 Yes | 29 No |
Answer / shanmu
Earth Resistance is measured by the device'EARTH MAGGER'.
Is This Answer Correct ? | 300 Yes | 121 No |
Earth resistance can be measured using Megger instrument.
Is This Answer Correct ? | 335 Yes | 180 No |
Answer / r.sarkar
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
Is This Answer Correct ? | 116 Yes | 19 No |
Answer / dinesh kumar
1.To measure earth resistance we use Earth Resistance
Meter/Megger.
2.In this Megger there are three terminals
Line,Nuetral&Earth.
3.Line & Nuetral are connected to two terminals and EARTH
Terminal to earth pit to be measured for resistance.
Is This Answer Correct ? | 169 Yes | 77 No |
Answer / ullas
using two methods:
1.fall of potential method
2.earth tester(device)
factors affecting earth resistance are
1. Shape & material of the earth electrode.
2. Depth of the electrode at which they r burried in soil.
3. Specific resistance of the soil surrounding the electrode
(Specific resistance of the soil varies depending on
moisture content in the soil..... varies from 80*10^3ohm-m
to 80*10^6ohm-m)
Is This Answer Correct ? | 74 Yes | 19 No |
Answer / k.viswanathan
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
Is This Answer Correct ? | 55 Yes | 12 No |
Earth resistance measured by using earth tester.
Is This Answer Correct ? | 40 Yes | 12 No |
Answer / natarajan
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
Is This Answer Correct ? | 24 Yes | 15 No |
want happens when a dc is given to a commutator
HOW TO CALCULATE HV CABLE SIZING?
What is star-delta transformer?
3.7 kw motor ,how much sq mm cabel want to bare this motor load
what will happen when a bulb s connected btwn two phases of a three phase delta connected source?
what types of fault occurred in transmission line ? which protection function senses the fault?
How to select a cable size for particular load?
0 Answers Amit Enterprises, Takasago Engineering, Techno Electric and Engineering,
what is through fault?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
in 3-phase transformer which type of transformet is used in output side?
what is the current law ?