Answer / chellappan
perfect zero value is not possible and near zero is
achievable in highly damp or watery surfaces
| Is This Answer Correct ? | 36 Yes | 0 No |
Answer / rajneesh babbar
if earth resistane value (0 ohm)not achived even all best
effort (using copper plate,best salution & charcoal
Ext.),joined more parallel earthings.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / chellappan s
It is thoritical and cannot be achieved. Acceptable value is 1 ohms for medium voltages by practice.
Still lower value may be archived by several methods where sentive equipments are to be earthed. It will be costlier.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shafi
It is desined by earthing calculation and practical
proved ,practical reading is taken in oil & gas area
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shafi
Yes, earthing rod should be inserted below 2meter summer
water level by drilling method
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / anand prasad yadav
depending on soil & best salution quiring in side the earth
pit.
| Is This Answer Correct ? | 2 Yes | 9 No |
Answer / rafiq
yes its possible to get earth resistance zero ohm
by using copper earthing (copper plate )
| Is This Answer Correct ? | 4 Yes | 18 No |
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
what is the difference between indoor package substation and outdoor
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
if we install two earth pits with a clear space of 5m without any interconnection,by checking the digital multimeter will it show continuity between earth pits? If so what would be the approx. value
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
Short circuit test of induction motor is carried out to compute= A stator resistance B rotor resistance C magnetizing reactance D stator reactance
What is the most accurate way of testing ELCB?ELCB is better than RCD?
MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?
when elecromagnatic waves are propogated in a wave guide?
what is a relay?
how to identify the cable quality and what is flame proof cable
how to handle 2500 kva transformar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)