I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
| Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
wat do knw aboot circuit breakers ?
1.Why sinle phase motor is not self starting 2.working principle of alternator 4.list out electrical formula
How to select earthing strip for 100kw induction motor ?
How can we calculate earth mat conductor size ..? & give the formula to determine earth conductor size?
In an alternator running with a balanced zero p.f. lagging load, phase differernc between the resultant armature flux and main field flux is always____? options is 180 degree....why?? explain.
Three way plug point is there ,in that plug why we need earth pin is bigger than compare with phase and nutral pins?
What is maximum demand and contract demand?
what does a string of resistors in a series will do?
Why we used 690V in ACS 800 drives.Why dont use standard voltage like 415v or 1.1Kv
the transient state stability limit of a system wherin power is transmitted throgh a double transmission line is (a)equal to steady state stability limit (b)more than its steady state stability limit (c)less than than its steady state stability limit (d)equal to its dynamic stability limit
why the manufacturer provide M and C terminals ? why they will not internally short them ?
We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)