I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
| Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
| Is This Answer Correct ? | 1 Yes | 0 No |
Design and explain a circuit to produce an unregulated full wave D.C supply.
why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
What is actual name of Transformer oil.
why protection meter is always connect to star
in conclusion why we select you?
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
what will be fault level of 11 KV , 2000 A ELECTRICAL SYSTEM?
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
What is the armature mmf in a D.C machine?
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
Generally in AC we consider voltage, frequency and phase sequence for parallel operation ... Can we parallel two DC battery chargers? If yes, then what precaution to be taken when we parallel two DC power?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)