Answer / satyajit sadhu

FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.

Is This Answer Correct ?    33 Yes 4 No

I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLE..

Answer / shivakumar kinni

1 MVA, 11/0.415kV Transformer

Full load current= 1000000/(1.732x415) = 1391.24A

% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)

Fault current= IFL/%Z =1391.24/0.05 =27.824 kA

Is This Answer Correct ?    18 Yes 3 No

I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLE..

Answer / mrudang

the above answer is right

Is This Answer Correct ?    10 Yes 3 No

I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLE..

Answer / raj l. lahare

For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.

Is This Answer Correct ?    1 Yes 0 No

I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLE..

Answer / deepak gupta

above ans. is right

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is the advantages of Lighting transformer?.. is it possible to reduce the power consumption ?.

6 Answers   Lucas TVS,


generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.

1 Answers   ETA, RRR, TCS,


What is precision of a measurement?

0 Answers  


Between Turbo alternator and Hydro alternator which one is more difficult to cool and why?

2 Answers  


what is the clear formula to calculate cable size for a load

0 Answers   TCS,






how many hvdc lines in india???

0 Answers  


Why Closing coli supervision is not required for Circuit breaker.

1 Answers   JSW,


how a DC clampmeter works if DC cant b step up r down?

1 Answers  


HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?

5 Answers  


(1) From the following option, which option is correct for largest size transformer.? a)1KVA,25Hz , b)1KVA,50HZ , c)1KVA,60Hz , d)1KVA,100Hz

5 Answers   Torrent Power,


In order that work may be done:(a) Two wires are necessary(b) The circuit must have a switch(c) Coal must be burnt(d) A supply of energy is required

1 Answers  


How the unidirectional torque produced in dc motor

2 Answers   CGL, Sail,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)