What is the use of arc chute in ACB?
Answers were Sorted based on User's Feedback
Answer / santosh kawade
Arc chute in ACB is use to increase lenght of arc, make it
weak and then extinguish the same.
santosh kawade
9224 69 3116
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / swapnil
arc chute in ACB is use to exingnuish the arc produce in
ACB .
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / bala guru nathan.v
The ARC chute model is the one way of extinguish ,it
seperates(widen) the bunch of flame ,the seperated flame
can be easily quenched by air ,if you understand the
function you should see the ACB Arch Chute once.
Is This Answer Correct ? | 8 Yes | 0 No |
The Arc chute in ACB is use to stop spread of Arc , make it
weak and than extinguish it.
and isolate from another live.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / rajkumar saini
Absorb the arc which is generate in contect point of ACB
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / nikunj
DG lube oil Specification is 15W/40
Difference between DG oil and Transformer oil is
DG oil is used for lubricating purpose because in DG Engine
lot of rotating parts are there,
Transormer oil Specification is 40KV and it is mineral oil
we are using oil in transformer for insulating and cooling
purpose
Is This Answer Correct ? | 2 Yes | 4 No |
Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?
What type of fittings and electrical accessories can be install in radiation area ?
Why 1/3 is used in symmetrical components?
what is form factor
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
If symmetrical fault occurs at the terminal of a synchronous motor then how the motor will act...explain it..
What is the difference between sensitive earth fault and restricted earth fault in power transformers?
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
what is the Transmission line differential protection and why differential protection also have backup Line Distance Protection ?
Can we use droop CT in neutral in place of W phase of alternator ?
which type of capacitors using in single phase motors
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???